Buried splice?
I have a 12-3 w/g wire (120v) running from a subpanel on the end of my house out to where we formerly had an above-ground pool. The line is run thru buried conduit to the end where it comes up to a receptacle box that sticks up about 15" above ground. I would like to extend that wire on out to provide service to another structure in the backyard, but would also like to do away with the receptacle box sticking up in the middle of the yard. Is there a safe and legal way to bury the splice?
PPBART is offline   Reply With Quote
Old 07-20-2012, 09:58 AM   #2
Licensed electrician
Rewards Points: 1,230
If this is UF cable, there are listed splice kits that can be buried.
If this is conduit with individual conductors you will need to extend the conduit and pull new conductors. A hand hole box would work also, but would need to be flush with the soil.
Old 07-20-2012, 09:59 AM   #3
TWX
Rewards Points: 35
I'm not a high voltage expert, but I gather that you'll need a pull box in the ground at the splice point and that you'll need the box/hole to be deep enough that you can support the splice case up off the ground so that when water gets inside, it doesn't interfere with the splice. I'm absolutely certain that there are electric codes on this though, and they should definitely be consulted.
I would also imagine that there are sealed splice cases available that can be direct-buried, but I would expect that those require a professional to be brought in.
TWX is offline   Reply With Quote
Old 07-20-2012, 01:11 PM   #4
PPBART's Avatar
Rewards Points: 303
Originally Posted by Jim Port View Post
If this is UF cable, there are listed splice kits that can be buried...
It is UF, and I think I'll try the splice kit approach -- thanks!
Old 07-20-2012, 01:51 PM   #5
joed's Avatar
Rewards Points: 11,964
If it is not UF then the wrong cable was used and it should be replaced.
Old 07-21-2012, 02:36 PM   #6
PPBART's Avatar
Rewards Points: 303
Even though it is in conduit it is required to be UF? I didn't know that.
Old 07-21-2012, 04:08 PM   #7
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Yes, the inside of conduit is not a location, so if the conduit is installed outdoors, it is still considered in a wet location.
Splice an Underground wire for light post rpearlberg Electrical 23 11-21-2011 06:49 PM
trenching near buried electric cable rizzo Landscaping & Lawn Care 9 04-22-2009 08:24 PM
Grinding stump but how deep are gas and electric lines buried? jbk Landscaping & Lawn Care 1 08-02-2008 12:46 PM
cable splice kit instead of juction box? pat72 Electrical 18 07-21-2008 06:12 PM