Originally Posted by Philly Master View Post
blue are 20's
all the rest COULD be 15 amp 14/2
dining room must be 20 amp 12/2
Hvac could be anything.... I wouldn't blanket statement a 30 amp circuit requirement...
Old 09-23-2013, 09:15 PM   #17
Rewards Points: 248
Originally Posted by rjniles View Post
You might want to consider box fill using all that #10 for receptacles and lighting circuits.
Hold your horses people. The plan was to use #10 to connect the main panel to 4-5 boxes distributed around the house. From there I was going to use #12 to connect receptacles and lighting circuits.
jackwashere is offline   Reply With Quote
Old 09-23-2013, 09:20 PM   #18
will you serve the #10 circuit with a 30 amp breaker? if yes and unless you have the appropriate breakers in these distributed 'boxes', you have a problem.
itsnotrequired is offline   Reply With Quote
Old 09-23-2013, 09:22 PM   #19
Rewards Points: 248
Originally Posted by stickboy1375 View Post
Just a little....but it's your money. Don't forget to weigh in the cost of labor for installing #10, it will offset the cost of installing #12 or #14 big time....
I'm doing the labor myself but I hear you. I figured $70 more one-time-cost to upgrade the cable a notch. I read somewhere that bigger cable is more efficient. However if the upgrade is going to be a nightmare I will back off and use #12 instead. It will make my life alot easier.
Old 09-23-2013, 09:23 PM   #20
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
hold your horses people. The plan was to use #10 to connect the main panel to 4-5 boxes distributed around the house. From there i was going to use #12 to connect receptacles and lighting circuits.
no ......
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 09-23-2013, 09:26 PM   #21
Rewards Points: 248
I meant boxes not sub-panels. Metal boxes about 4x4 inches with knockouts and covers. Clamps tie the icoming and outgoing romex to the box.
I was only going to use #10 on 20 amp circuits because I read that it is more efficient to use bigger wires. For no other reason.
Old 09-23-2013, 09:28 PM   #22
the extra electricity loss on #10 vs #12 recep/lighting circuits will amount to maybe 2 or 3 cents a year. 1000% not worth it.
Old 09-23-2013, 10:21 PM   #23
Rewards Points: 6,652
You did not just state that. I see no way that this is going to pass code, let alone the fact that it is placing a lot of unneeded resistance on each circuit.
Where did you come up with that it is okay to wire branch circuits in this manner? I would only do something like this, if I was wiring Isolation transformers on a 240vAC circuit, for audio or video distribution, or for a panel for use as lighting control.
Old 09-24-2013, 05:21 AM   #24
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Where did you come up with that it is okay to wire branch circuits in this manner? .
From other posts by this user, I have a feeling I know what he is trying to do, however, there is nothing to prohibit using 10/2 for general purpose branch circuits.
The Following User Says Thank You to k_buz For This Useful Post:
stickboy1375 (09-24-2013)
Old 09-24-2013, 06:01 AM   #25
E2 Electrician
The OP's method is perfectly acceptable and allowed by code
The OP is trying to eliminate voltage drop, nothing more....
Old 09-24-2013, 07:42 AM   #26
joed's Avatar
Rewards Points: 12,442
You can not feed receptacles with anything larger than a 20 amp circuit. There would be no chance of an upgrade needed in the future. #12 is all you will ever need.
You are over thinking, over complicating, and over spending this project.
Old 09-24-2013, 08:29 AM   #27
in the states you can but i don't know what anyone would ever want to. all the receps would need to be rated 30 amp and the plug configurations wouldn't work with anything you would normally plug into a standard wall recep.
Old 09-24-2013, 12:26 PM   #28
joed's Avatar
Exactly. You can't install a standard duplex receptacle on a 30 amp circuit. Don't know about lighting in US, But in Ontario you must have lighting on a 15 amp circuit.
Old 09-24-2013, 01:09 PM   #29
The OP's method is perfectly acceptable and allowed by code. The OP is trying to eliminate voltage drop, nothing more....
Yes you can use #10 by code, but there is not enough length to qualify this as being a circuit with a large drop, to need #10. That is what the whole argument is about, is why the OP believes they need to pull a bunch of #10 to the branch circuits.
Is it because they have thousands of feet just laying around, and feel the need to use it, or something that they read somewhere, that they think the few tens of feet, qualified for the #10 on the circuit.
Old 09-24-2013, 04:37 PM   #30
E2 Electrician
I don't really get why everyone is against the OP, it's his money, he can spend it as he sees fit.... I do jobs that are spec'd out for #12 AWG for lighting, I think that is just about as big as a joke as using #10.... everyone needs to relax around here and keep it to code, and fewer opinions.
Identify age of old Romex - also funny ground Leah Frances Electrical 9 02-06-2012 12:07 AM
How to build a romex spinner jimmy21 Electrical 17 02-06-2012 12:01 AM
bundling romex mazey Electrical 3 09-08-2011 07:05 PM
romex clamped against bx knockout in old box kbm774 Electrical 11 08-16-2010 01:53 PM
bundling romex, code? johnnyboy Electrical 6 10-09-2007 05:57 AM