Broken Tab In Blue Box - Violation? - Electrical - DIY Chatroom Home Improvement Forum
Old 01-23-2011, 04:10 PM   #1
Rewards Points: 150
Broken tab in blue box - violation?
Will a broken off tab in a blue box be a code violation?
sheslostcontrol is offline   Reply With Quote
Old 01-23-2011, 04:47 PM   #2
Journeyman Wireman
Rewards Points: 150
Depends on your AHJ. At the very least, the electrical cable will need to be fastened within 8 inches of the box. It may also require that the knock-out be filled with some sort of fire caulking/barrier.
Jupe Blue is offline   Reply With Quote
Old 01-23-2011, 05:07 PM   #3
Rewards Points: 150
Yeah, all of the wires are stapled within 6-8" of the boxes. thanks for the reply.
Old 01-23-2011, 05:10 PM   #4
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
yes, it is a violation. It leaves too large of a hole in the box. On top of the electrical code issues, it also destroys the fire rating.
Old 01-23-2011, 05:28 PM   #5
Household Handyman
Rewards Points: 1,408
Only if you get caught Sir, only if you get caught.
Old 01-23-2011, 05:37 PM   #6
I agree with Thurman. Fire ratings on plastic boxes with tabs always seemed a little bit silly to me.
If I have a 12/2 and a 12/3 going into the box thru the same tab is it gonna be a little safer than if I have one 14/2?
I've yet to receive a red tag for a missing tab. I've yet to have an inspector seek one out for that matter.
AndyinAtl is offline   Reply With Quote
Old 01-23-2011, 06:06 PM   #7
nap
You talking to me?
nap's Avatar
It's always a violation. Getting caught makes it a red tag fix it violation.
Old 01-23-2011, 06:48 PM   #8
Remodeler
adpanko's Avatar
Rewards Points: 150
Just a clarification question
Some plastic boxes have the clamp-like closures that hold the cable coming into the box. But other plastic boxes, specifically most of the Carlon single gang boxes, have full knockouts and don't require any clamping mechanism for the cable. You just have to fasten the cable to the framing member within a few inches from the box. If you run a 14/2 cable into one of those knockout openings, more than half area of the knockout is still open, therefore an opening for flames to get through. This is not a code violation, correct? But if you have one of the other knockouts knocked out and no cable running through it, that is a violation, right?
adpanko is offline   Reply With Quote
Old 01-23-2011, 07:01 PM   #9
nap
You talking to me?
nap's Avatar
depending on the size of the box, that may not be a proper method of installing the cable. In boxes 2 1/4X 4 or smaller, the cable is not required to be secured to the box. In anything larger than that, it must be.
additionally, the code gives this ambiguous direction concerning openings:
"openings through which conductors enter shall be adequately closed"
I can't find it but for some reason I remember something like you cannot have any openings greater than 1/4". I can't defend that though.
Old 01-23-2011, 07:50 PM   #10
It's weird. In commercial work it would be an unforgivable sin to install a 1900 box with an open knockout. In resi work if I have to replace an existing plastic box with another I will destroy the clamps on the box to facilitate the wires going back in w/out a twinge of guilt.
I understand the thinking about fire ratings on boxes but the way they are designed just doesn't make sense. I am a part time supervisor for Habitat for Humanity and I go into great detail explaining to the volunteers the logic behind why requiring all the holes drilled through the top plate and bottom plate of a stud wall have to be filled with a fire blocking material is so important. If a fire starts in a box due to poor wiring the way the plastic boxes are designed will not starve the fire of oxygen. What is critical is restricting the supply to just that one stud space.
Andy-n-ATL is offline   Reply With Quote
Making a patio from broken granit slabs need help BJLower Tiling, ceramics, marble 9 09-15-2014 12:15 PM
Should I replace my blue board after it got wet from a water heater leak? petep Drywall & Plaster 4 07-11-2010 09:44 PM
Fanimation ceiling fan question: no blue wire from ceiling camrn2006 Electrical 8 03-07-2010 12:19 AM
Got a dark blue mess on my hands... pk1023 Painting 6 09-14-2009 08:30 PM
Semi gloss on Semi gloss mattpricemn Painting 6 08-25-2008 07:18 PM