installing a residential 4 ton central AC unit. Name plate states 240V, MCA= 26A, MOP= 45A. The AC unit will be approximately 70 feet from the main distribution panel. I've reviewed NEC & table 310.16, and not sure what size breaker and wire size (45A & #8 wire- 2 conducter, 1 ground)??
any help please?
thank you
Rob
RLTW
rcassidy is offline   Reply With Quote
Old 05-06-2013, 10:52 AM   #2
Rewards Points: 6,652
The plate on the ac unit should state max amp. That is what you go by.
Old 05-06-2013, 05:45 PM   #3
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
10's on a 40 amp breaker.
The Following User Says Thank You to k_buz For This Useful Post:
MTN REMODEL LLC (05-06-2013)
Old 05-06-2013, 05:48 PM   #4
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
#10's on a 40 amp breaker is my vote as well....
Originally Posted by rcassidy View Post
installing a residential 4 ton central AC unit. Name plate states 240V, MCA= 26A.
310.16 allows 35 amps on #10 AWG
MOP= 45A.
40 amp breaker is more common than a 45A breaker, and will not be an issue for your installation.
Old 05-06-2013, 11:56 PM   #5
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
For sizing what? The wire or the breaker?
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 05-07-2013, 07:27 AM   #6
Rewards Points: 720
I've never seen "max amp" on an AC nameplate. The closest thing to that would be the locked-rotor amps (LRA) and that is NOT what you use to size the conductors or the OCPD.
The nameplate should include the following. Two of which are used to select the right conductors and OCPD:
"Maximum Fuse Size" or "Maximum Fuse or Circuit Breaker Size" (Note: For the former, you have to have fuses on the circuit) (Abbreviated MOP)
"Minimum Circuit Ampacity" (Abbreviated MCA)
"Locked Rotor Amps" (Abbreviated LRA)
Don't confuse LRA with RLA that might also be on the nameplate. The RLA is the Running Load Amps and that is the normal current draw of the unit. The MCA is figured from the RLA.
Mark
busman is offline   Reply With Quote
The Following 3 Users Say Thank You to busman For This Useful Post:
electures (05-07-2013), mm11 (05-07-2013), stickboy1375 (05-07-2013)
Old 05-07-2013, 12:02 PM   #7
The breaker. I was at work and posting during break, so did not have time to go into much detail. Also hate trying to post from the iPhone, because the keyboard on those things are not made for adults.
Old 05-07-2013, 12:09 PM   #8
Busman, mine has min & max amp rating, min & max voltage on the nameplate, also both my neighbors have the min & max amp/volt rating on the plates. As for the OP, 40 amps is a large amount for a unit. I am either guessing a unit with a heater, large btu size, packaged unit, or older unit.
I ended up pulling #10 for my unit, because at the time, we were looking at both heat pumps & a/c units, and ended up getting a good deal on a 13seer Armstrong a/c unit, that someone had ordered, but never got picked up, so my guy that does my hvac, got it at about half off, due to the warehouse that he gets all his hvac stuff from here in town, could not send it back to Armstrong, and wanted to get it out of the shop.
If I ever go with a heat pump, easy change over from a 20 amp breaker to 30 amp, because I already have the #10 pulled.
Old 05-07-2013, 12:34 PM   #9
Rewards Points: 720
Yes, there are a lot of other numbers on most nameplates. I only bothered to cover the ones of interest to the OP. You mention that yours has min and max amp rating. I'm going to bet that that is min and max OCPD size. To call is "amp rating" is confusing. It's true that the rating of a branch circuit is determined by the rating of the OCPD, but I think it's less confusing to call it the required sized of the OCPD.
The only thing the OP really need to know is that the conductors need to meet or exceed the MCA when properly adjusted and derated and the OCPD needs to be between the minimum and maximum OCPD values listed and it needs to be the proper type (fuse or circuit breaker). He then just needs to account for voltage drop.
Mark
Old 05-07-2013, 12:51 PM   #10
That is true on the voltage drop. Of course, most would have just gone out and got the #8 and not think about it. It would have cost them a little more, but would not have done any damage going with the larger size wire, other than their pocket book.
Breakers, wire size and new heat pump ACR_SCOUT Electrical 21 01-29-2012 03:25 PM
Correct wire size? fatczech Electrical 6 12-18-2011 09:15 PM
20A Breaker, 14 gauge wire? joside Electrical 12 08-25-2010 10:41 AM
wire size for ac/heating forced air unit macfluke Electrical 2 03-04-2009 01:29 AM
What size wire and what kind of conduit... epeterson777 Electrical 15 02-21-2009 08:43 PM