i just replaced pool pump motor (ao smith)new one keeps tripping breaker box, only difference is old motor max amp was 18.6/9.3 and new one is 22.0/11.0 , the breakers are two 20 amps, is this my problem, do i need bigger breakers?
hllanes is offline   Reply With Quote
Old 10-10-2012, 07:53 PM   #2
Electrical Contractor
kbsparky's Avatar
Do you have a motor wired for 120 Volts connected to a 240 Volt source?
That would trip it out.
Keep resetting it and you'll burn the motor out in short order .... (let the smoke out as they say)...
-KB
Old 10-11-2012, 05:06 AM   #3
dmxtothemax's Avatar
Rewards Points: 5,372
If the new one is 22.0a and your running it on 20a breakers
WELL THERE'S YOUR PROBLEM !
Bigger breakers,
make sure the cables can handle the extra load first !
dmxtothemax is offline   Reply With Quote
Old 10-11-2012, 05:52 AM   #4
Electrician
Rewards Points: 150
Dmxtothemax is a little off. The first, larger number is the 120v amp draw. The smaller number is the 240v amps. Kbsparky is correct. A breaker that has two levers with a handle tie between them, or as you say "two 20 amps", is 240v. That's the second number, 11 amps, well under your breaker rating. Check the wiring diagram on the motor. Then remove the access cover to make sure the jumpers are on the right spade lugs for 240v. Also, make sure you didn't pinch a wire under the cover and make a short to metal.
Glennsparky is offline   Reply With Quote
Old 10-11-2012, 07:11 AM   #5
biggles's Avatar
drain the impeller of the pumpa and restart it might be the initial locked rotor start load tripping the breaker with the water load to pump on it..if it runs with no water you need a bigger breaker.the lower amp rating is for 240V and the other is for 115V off the tag
Old 10-11-2012, 07:29 AM   #6
joed's Avatar
Rewards Points: 12,926
Check the voltage setting. I suspect the motor came defaulted to 120 volts.
Old 10-11-2012, 10:02 AM   #7
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
What is the horsepower rating of the motor?
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 10-11-2012, 05:55 PM   #8
Even at 11a, if it is just the running current,
This could mean a starting current that could easily exceed 20A.
Unless it is a time lag breaker.
Old 10-12-2012, 01:03 AM   #9
Semi-Pro Electro-Geek
Rewards Points: 2,942
But it would have to be way higher (at least 30-40A) to trip it instantly. An 11A centrifugal pump motor really should start on a 20A breaker.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Garage Heater Trips Breaker Pacodeveux Electrical 7 12-12-2011 09:41 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
Update: Power on several circuits comes and goes all at once, never trips breaker Michael H Electrical 9 07-03-2009 10:12 PM
20 Amp Breaker only trips once in a while panhandlion Electrical 14 11-26-2007 08:36 PM
Main Breaker Trips Repeatedly kkf Electrical 7 06-18-2007 04:31 PM