I am having problems with the breaker tripping for my Hayward pool pump. Ran great last year. Pump is about 4 years old. It will run for about 10 to 15 seconds and then the breaker trips. Replaced the breaker with the same results. Pump motor is not hot and seems to be running normal when it trips.
saxd9521 is offline   Reply With Quote
Old 05-27-2013, 08:08 AM   #2
joed's Avatar
Rewards Points: 13,332
Is the breaker a GFCI. It could be water in the pump. The pump motor could be bad now even though it was fine last year.
Old 05-27-2013, 12:11 PM   #3
Rewards Points: 1,192
Try running pump valved off.(No load).
bobelectric is offline   Reply With Quote
Old 05-27-2013, 02:08 PM   #4
Semi-Pro Electro-Geek
Rewards Points: 2,970
If the breaker is not a GFCI, then the problem may be the centrifugal switch which disconnects the starting winding. If it fails, the motor an draw very high current and trip the breaker. If it's a GFCI breaker, the problem is probably a ground fault and the motor may need to be replaced.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
micromind (05-27-2013)
Old 05-27-2013, 04:07 PM   #5
Idiot Emeritus
Rewards Points: 1,492
My thoughts as well.
Usually if there's a ground fault in the motor, the GFI will trip instantly, but not always.
If the start winding is not de-energized when the motor is up to speed, it'll usually trip a breaker before the overload.
Centrifugal switches are notorious for getting stuck after a motor has not been run in a long time. Especially an open motor that is run outside.
Rob
micromind is offline   Reply With Quote
Circuit breaker keeps immediately tripping after reset... Ler0y Jenkins Electrical 30 05-22-2013 01:17 PM
GFCI Breaker Tripping orloosem Electrical 0 05-12-2013 10:21 AM
sump pump keeps tripping breaker after about 5 minutes of running DanDaMan Electrical 9 04-21-2011 11:32 PM
Heat Pump trips breaker gt1935 HVAC 2 03-26-2011 10:06 PM
Breaker Keeps Tripping mxingislife Electrical 33 01-12-2011 10:11 AM