Breaker Size for a Sauna Heater


Planning to install a sauna heater with the following specifications:
5 KW
20.8 AMP
240 Volts

I have an existing 10/3 wiring that can be used to hook up the sauna heater to the Circuit breaker.

What amperage breaker size should I use for this connection?
Is a 10/3 cable sufficient for this type of sauna heater?

Appreciate your help!

atm is offline   Reply With Quote
Old 10-12-2012, 01:59 PM   #2
Member
 
joed's Avatar
 
Join Date: Mar 2005
Location: Welland, Ontario
Posts: 7,222
Default

Breaker Size for a Sauna Heater


30 amp breaker on the 10/3 cable will be fine. The heater likely only uses two of the wires for 240 volts. Simply cap of the white wire and leave it in the box.

__________________
Do not PM with questions that can be asked in a forum. I will not respond.
joed is online now   Reply With Quote
Old 10-13-2012, 06:11 AM   #3
atm
Newbie
 
Join Date: Mar 2009
Posts: 29
Default

Breaker Size for a Sauna Heater


Thank you.

What would be the effect if a 20 amp breaker was used?
atm is offline   Reply With Quote
Old 10-13-2012, 06:51 AM   #4
Member
 
Join Date: Sep 2008
Location: Oregon
Posts: 1,497
Default

Breaker Size for a Sauna Heater


Does the manufacturer's installation instructions say which size and type of breaker to use?
Billy_Bob is offline   Reply With Quote
Old 10-13-2012, 11:04 AM   #5
atm
Newbie
 
Join Date: Mar 2009
Posts: 29
Default

Breaker Size for a Sauna Heater


No it does specify any breaker size. I was just wondering what happens if 20 amp breakers are used?
atm is offline   Reply With Quote
Old 10-13-2012, 11:10 AM   #6
Licensed Electrician
 
k_buz's Avatar
 
Join Date: Mar 2012
Location: SE Wisconsin
Posts: 4,246
Default

Breaker Size for a Sauna Heater


Quote:
Originally Posted by atm View Post
No it does specify any breaker size. I was just wondering what happens if 20 amp breakers are used?
They will trip.
__________________
__________________________________________________ ______________
Answers based on the National Electric Code. Always check local amendments.


k_buz is offline   Reply With Quote
Old 10-13-2012, 12:05 PM   #7
E2 Electrician
 
stickboy1375's Avatar
 
Join Date: Apr 2012
Location: Litchfield, CT
Posts: 4,261
Default

Breaker Size for a Sauna Heater


Quote:
Originally Posted by k_buz View Post
They will trip.
Unlikely at 20.8 amps.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
stickboy1375 is offline   Reply With Quote
Old 10-13-2012, 12:14 PM   #8
Licensed Electrician
 
k_buz's Avatar
 
Join Date: Mar 2012
Location: SE Wisconsin
Posts: 4,246
Default

Breaker Size for a Sauna Heater


Quote:
Originally Posted by stickboy1375 View Post
Unlikely at 20.8 amps.
If it runs at 20.8 I would suspect it would trip. If it occasionally hits 20.8 then I suspect it will not.
__________________
__________________________________________________ ______________
Answers based on the National Electric Code. Always check local amendments.


k_buz is offline   Reply With Quote
Old 10-13-2012, 02:36 PM   #9
E2 Electrician
 
stickboy1375's Avatar
 
Join Date: Apr 2012
Location: Litchfield, CT
Posts: 4,261
Default

Breaker Size for a Sauna Heater


Quote:
Originally Posted by k_buz View Post
If it runs at 20.8 I would suspect it would trip. If it occasionally hits 20.8 then I suspect it will not.
It would never trip at 20.8 amps...

The UL standard permits an OCPD to carry 134% of the device rating forever. It has to trip in no more than 60 minutes for 135% load.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
stickboy1375 is offline   Reply With Quote
The Following User Says Thank You to stickboy1375 For This Useful Post:
mpoulton (10-13-2012)
Old 10-13-2012, 03:23 PM   #10
DIY Enthusiast
 
sublime2's Avatar
 
Join Date: Mar 2012
Location: New Jersey
Posts: 1,061
Default

Breaker Size for a Sauna Heater


Quote:
Originally Posted by stickboy1375

It would never trip at 20.8 amps...

The UL standard permits an OCPD to carry 134% of the device rating forever. It has to trip in no more than 60 minutes for 135% load.
Does that mean it would need 26.80 amps before it would trip?
sublime2 is offline   Reply With Quote
Old 10-13-2012, 03:24 PM   #11
E2 Electrician
 
stickboy1375's Avatar
 
Join Date: Apr 2012
Location: Litchfield, CT
Posts: 4,261
Default

Breaker Size for a Sauna Heater


Quote:
Originally Posted by sublime2 View Post
Does that mean it would need 26.80 amps before it would trip?
Maybe, maybe not, depends on the actual trip curves of the manufacture, but, this is how UL tests a molded case breaker.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
stickboy1375 is offline   Reply With Quote
Old 10-13-2012, 07:37 PM   #12
Member
 
joed's Avatar
 
Join Date: Mar 2005
Location: Welland, Ontario
Posts: 7,222
Default

Breaker Size for a Sauna Heater


Depends on the breaker. I would NEVER put a known 20.8 amp load on a 20 amp breaker.
__________________
Do not PM with questions that can be asked in a forum. I will not respond.
joed is online now   Reply With Quote
The Following User Says Thank You to joed For This Useful Post:
k_buz (10-13-2012)
Old 10-13-2012, 08:02 PM   #13
E2 Electrician
 
stickboy1375's Avatar
 
Join Date: Apr 2012
Location: Litchfield, CT
Posts: 4,261
Default

Breaker Size for a Sauna Heater


Quote:
Originally Posted by joed View Post
Depends on the breaker. I would NEVER put a known 20.8 amp load on a 20 amp breaker.
Neither would I, and that was never my intent, I was just sharing the true facts of UL standards.

__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
stickboy1375 is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Heater Tripped Breaker lmark103 Electrical 1 09-28-2012 04:40 PM
breaker size for old knob and tube Sandra Murdock Electrical 2 04-21-2012 01:49 PM
Garage Heater Trips Breaker Pacodeveux Electrical 7 12-12-2011 09:41 PM
wire size vs breaker size Jimster 481 Electrical 3 08-20-2011 09:41 AM
Heater causes breaker to hum oakwood02 Electrical 3 01-03-2008 06:50 PM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.