Breaker Size for a Sauna Heater
Planning to install a sauna heater with the following specifications:
5 KW 20.8 AMP 240 Volts I have an existing 10/3 wiring that can be used to hook up the sauna heater to the Circuit breaker. What amperage breaker size should I use for this connection? Is a 10/3 cable sufficient for this type of sauna heater? Appreciate your help! |
30 amp breaker on the 10/3 cable will be fine. The heater likely only uses two of the wires for 240 volts. Simply cap of the white wire and leave it in the box.
Thank you and question
Thank you.
What would be the effect if a 20 amp breaker was used? |
Does the manufacturer's installation instructions say which size and type of breaker to use?
No it does specify any breaker size. I was just wondering what happens if 20 amp breakers are used?
The UL standard permits an OCPD to carry 134% of the device rating forever. It has to trip in no more than 60 minutes for 135% load. |
Depends on the breaker. I would NEVER put a known 20.8 amp load on a 20 amp breaker.