Breaker & Fuse Math - Electrical - DIY Chatroom Home Improvement Forum
Old 06-30-2012, 09:08 AM   #1
JPM
Bill Traver
Rewards Points: 93
Breaker & Fuse Math
I have an older house ... it has 100 AMP service coming in from the street. The wiring is mixed (old and some new). Right now, the panel has 2 50 AMP fuses then 4 fuses to tie in circuits. They are all 15 AMP.
I am thinking of switching to Fuses. If I have 100 AMP service coming in, can I switch to 2- 20 AMP breakers (pull 12 ga wire) and 4 - 15 AMP breakers (total is 100, but not sure if I need to stay lower than that). OR Can/Should I just go with 6 - 15 AMP?
This stems from having issues time to time with older AC units plugged in (SEE SEPERATE THREAD for question on this).
Thanks!!
JPM is offline   Reply With Quote
Old 06-30-2012, 09:20 AM   #2
Rewards Points: 1,442
The total of the branch circuit breakers does not have to stay lower than 100 or whatever.
The individual branch circuit breakers can stay the same (15 amp for each with 14 gauge wiring, 20 amp for circuits with all 12 gauge wiring).
Only if the existing panel is rated (see its label) for 100 amps then can substitute two 100 amp fuses for the two 50 amp fuses in the main disconnect block. (Or 75 amp fuses for a 75 amp rated panel.) Alternatively install a new 100 amp panel and put a 50 amp double breaker in it to feed the old panel as a subpanel.
You can add more breakers to the existing panel (or add a subpanel) with additional 15 and 20 amp branch circuits (or 10 gauge wiring for 30 amp circuits, etc.) even if the main fuses are still 50 amp, subject to any load calculation required as part of your electrical construction permit. Because all branch circuits are not going to be fully loaded at the same time, the sum of the branch circuit breaker ratings can be much greater than the main breaker or fuse rating.
But in those less common situations where one meter feed goes to two panels with first disconnecting means inside those panels and neither is a subpanel of the other, the sum of their top breaker/fuse ratings may not exceed the service amperes rating. (A 100 amp 120/240 volt service provides 100 amps on each hot leg.)
Outside breaker, inside main breaker panel, so is it a sub? CPF Electrical 29 02-01-2012 11:28 AM
Fuse panel main breaker question cjm94 Electrical 5 11-16-2011 10:16 AM
Upgrading 60a fuse -> 100a breaker, grounding bx cable? njoel Electrical 3 03-18-2010 04:22 PM
small voltage on circuit with breaker off jasonmechler Electrical 3 08-24-2009 09:52 AM
Fuse / Breaker Mix Beren Electrical 2 05-26-2007 07:49 PM