Breaker & Wire Size - Electrical - DIY Chatroom Home Improvement Forum
Old 10-25-2012, 02:21 PM   #1
breaker & wire size
Am installing GE JSR06B single oven in base cabinet. Tag says 3.4 KW @240 volts. What is proper wire and breaker size? I am 50 feet from panel.
Herb Shearmire is offline   Reply With Quote
Old 10-25-2012, 02:37 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,948
I'd use #12 on a 20A breaker.
Speedy Petey is online now   Reply With Quote
Old 10-25-2012, 02:53 PM   #3
Rewards Points: 660
Just for lurkers who want to learn, do you mean 12-3 NM Speedy?
Can you tell from the OP post how much amperage the oven uses?
Does it matter if it is 120 or 240?
B
Beepster is offline   Reply With Quote
Old 10-25-2012, 03:02 PM   #4
Semi-Pro Electro-Geek
Rewards Points: 2,922
3400W / 240V = 14.2A. A 15A breaker and #14 wire could legally be used since an oven is not a continuous load, but a 20A breaker and #12 is probably a better choice. Since many ovens require a 30A circuit, running #10 wire might not be a bad idea for future compatibility if the oven is ever replaced. You could run 2-conductor (with ground) NM cable, but it would be nice to use 3-conductor in case a future replacement oven requires 120/240. So while you could get away with 14-2 NM and a 15A breaker, 10-3 NM and a 30A breaker would be good to have in case the oven is ever replaced.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 10-25-2012, 03:29 PM   #5
Oso954's Avatar
Rewards Points: 1,020
I don't think running 2-conductor (with ground) is code compliant.
Oso954 is online now   Reply With Quote
Old 10-25-2012, 03:36 PM   #6
Why not??
Old 10-25-2012, 03:49 PM   #7
Licensed electrician
Rewards Points: 1,502
Perfectly fine for a straight 240 load.
Old 10-25-2012, 03:53 PM   #8
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
There is a huge price difference between 12/2 and 10/3. That combined with the fact that most free standing ranges are 120/240V 40A (min), I would run 12/2 in this case without hesitation.
Old 10-25-2012, 03:56 PM   #9
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,192
An oven that requires 240 volts at 3.4 KW (14+ amps), a 2 wire + ground circuit with #12 conductors is more that sufficient. This can be a 12-2 cable or individual conductors in conduit.
Coastal South Carolina
Old 10-25-2012, 06:12 PM   #10
Oso954's Avatar
Why not??
A new circuit installation for a range (with receptacle) must be 3 plus ground and use 4 prong plug. I assume a wall oven would have to also meet that requirement, if a receptacle is used.
I am not sure of the hard wire requirements. Is that the difference ?
The other item that could impact it would be installing per manufacturer instructions.
Old 10-25-2012, 06:18 PM   #11
What if the range or other appliance is straight 240V?
You are putting a blanket statement on this that is NOT true. It is true for a 120/240V range, but not for just a "range" or "oven". MANY ovens & cooktops are straight 240V that do not have a neutral thus not requiring a "4-wire" feed.
Old 10-25-2012, 07:59 PM   #12
Master Electrician
Rewards Points: 3,824
Electrical requirements are 120/240 volt circuit per manual.
brric is online now   Reply With Quote
The Following 2 Users Say Thank You to brric For This Useful Post:
mpoulton (10-25-2012), Speedy Petey (10-25-2012)
Old 10-25-2012, 10:50 PM   #13
To the OP: This means you must use 3-conductor cable with ground (red, black, white, and bare) instead of 2-conductor.
The Following User Says Thank You to mpoulton For This Useful Post:
brric (10-26-2012)
Breakers, wire size and new heat pump ACR_SCOUT Electrical 21 01-29-2012 02:25 PM
Correct wire size? fatczech Electrical 6 12-18-2011 08:15 PM
20A Breaker, 14 gauge wire? joside Electrical 12 08-25-2010 09:41 AM
Wire Needed for GF / Arc Fault breaker jamiedolan Electrical 13 09-20-2009 08:15 AM
wire size for ac/heating forced air unit macfluke Electrical 2 03-04-2009 12:29 AM