Brassie - Electrical - DIY Chatroom Home Improvement Forum
Old 11-14-2011, 09:33 AM   #1
Smile
Brassie
In order to run romex 40A 3 wire + grd out side from basement to second floor kitchen in 3/4" PVC should I strip jacket from romex or is it ok to leave it on? I was told it might cause to much heat inside PVC.
Brassie is offline   Reply With Quote
Old 11-14-2011, 09:35 AM   #2
Just call me Andrew
Rewards Points: 1,020
You cannot ever strip the sheathing off romex and run the bare conductors.
You cannot use romex outside.
You have to use indivudal THWN wires or UF wire. I'd use THWN, UF too hard to pull through conduit.
Andrew
secutanudu is offline   Reply With Quote
The Following User Says Thank You to secutanudu For This Useful Post:
Jim Port (11-14-2011)
Old 11-14-2011, 09:51 AM   #3
If you strip the outter jacket they become
Thhn conductors. It's just fine to remove the outter jacket.
Colomboj is offline   Reply With Quote
The Following User Says Thank You to Colomboj For This Useful Post:
Brassie (11-14-2011)
Old 11-14-2011, 09:53 AM   #4
Just call me Andrew
1. not necessarily correct
2. THHN cannot be used outdoors in conduit.
Andrew
Old 11-14-2011, 10:02 AM   #5
Licensed electrician
Rewards Points: 1,634
Absolutely wrong. The conductors are not labeled so you cannot assume they are THHanything.
The NM is listed as an assembly. Removing the outer jacket destroys the listing of that assembly.
The Following 7 Users Say Thank You to Jim Port For This Useful Post:
a7ecorsair (11-14-2011), Brassie (11-14-2011), frenchelectrican (11-15-2011), mpoulton (11-14-2011), SD515 (11-14-2011), secutanudu (11-14-2011), Speedy Petey (11-14-2011)
Old 11-14-2011, 10:13 AM   #6
Thanks for the quick reply from all. Very helpfull--Breassie