Box Sizing - Electrical - DIY Chatroom Home Improvement Forum
Old 09-05-2012, 12:03 PM   #1
Box sizing
I am doing some box sizing calculations, and am a little stumped.
Lets say you have a receptacle which pigtails to another receptacle. So you have power in, power out, and the device.
By my calculations this is:
4 - hots and neutrals
1 - ground
1 - clamps
2 - device
= 8
If its all #14 then you need 16 cu.in box. Most standard receptacle boxes are 12.5 cu.in.
http://www.homedepot.ca/product/devi...-welded/914369
Does this mean that a standard box cannot even be used unless its an end point? Am I missing something?
zubor is offline   Reply With Quote
Old 09-05-2012, 02:11 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 546
In Canada you have to figure the wire nuts also.
That box with a 14/2 feed would have 2+2+2+2+4=12 cu.
2 for the hot, 2 for the neutral, 2 for the ground, 4 for the device, and 2 for the internal clamp.
You need to double your hot and neutral from 4 to 8 since you have an in and out cable, so the min. box is 16 cu.
jbfan is online now   Reply With Quote
Old 09-05-2012, 03:10 PM   #3
I can't seem to find any mention of clamps or ground wires in the CEC
Only 1 for every insulated conductor, 1 for every pair of wire nuts, 2 for every device
Old 09-05-2012, 03:39 PM   #4
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
That is not a standard box in the US, and I doubt it is a standard box in Canada.
Properly Sizing a Water Softener zerious Plumbing 33 05-15-2012 06:32 PM
Cabin Roof Design and Beam Sizing RCNC225 Building & Construction 0 01-25-2012 10:54 AM
Sizing a dual shut off valve for a water line to fridge ericman Plumbing 10 08-19-2011 09:47 PM
Sizing Motor Branch Circuit Conductors and OCPD's electures Electrical 5 06-22-2011 11:32 PM
Sizing a furnace - can't find one small enough Jim W HVAC 30 05-13-2009 08:38 PM