Old 06-28-2007, 04:06 AM   #1
Box fill conductor count
I have been researching this question, but have not found it unambiguously addressed.
For box-fill calculations, in a junction box, if I splice an incoming conductor to an outgoing conductor, do I now have two conductors or one?
Doug_Shaver is offline   Reply With Quote
Old 06-28-2007, 07:10 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
It's confusing, but clear if you read it closely:
(1) Conductor Fill
Each conductor that originates outside the box and terminates or is spliced within the box shall be counted once, and each conductor that passes through the box without splice or termination shall be counted once. A looped, unbroken conductor not less than twice the minimum length required for free conductors in 300.14 shall be counted twice. The conductor fill shall be calculated using Table 314.16(B). A conductor, no part of which leaves the box, shall not be counted.
A wire ending in the box, be it spliced, capped, etc. Counts ONE.
A wire passing clean through the box, no loop or slack. Counts ONE.
A wire passing through the box, with enough slack to be cut and spliced. TWO conductors.
Your question would have two of the first example.
Old 06-28-2007, 10:25 AM   #3
Here's link that explains it as well.
http://www.taunton.com/finehomebuild...ger-boxes.aspx
It takes less time to do a thing right than it does to explain why you did it wrong.
-Henry Wadsworth Longfellow
beer_geek is offline   Reply With Quote
Old 06-28-2007, 12:21 PM   #4
Yes, that is clear enough. I don't have a code book, and couldn't find a site that quoted it on this topic. Not that I spent a LOT of time looking . . . .
Thank you very much.
Last edited by Doug_Shaver; 06-28-2007 at 12:22 PM. Reason: Inadvertent deletion before posting.
Old 06-28-2007, 12:35 PM   #5
Thank you. I found that page during my research. From it, I inferred what the answer to my question probably was. But, since it assumed the installation of a receptacle, and the box in question won't have any devices, I wanted to double-check.
Routing an oil fill? sandyman720 HVAC 1 03-07-2007 11:25 AM