Are my box-fill calculations correct?
(1) 4-gang switch box = 63.5 cu. in. (stamped on inside)
(3) #12/3 BX = 13.5 (6 x 2.25)
(2) #12/3 NM = 9.0 (4 x 2.25)
(4) Dimmer Switches = 9.0 (4 x 2.25)
Largest GND Wire is #12 = 2.25
Total Volume Required = 33.75 (29.75 spare)
Notes:
1. The third wire in each cable group is the ground. From what I've read you are only required to count one (1) ground and that needs to be the largest ground wire in the box.
2. There are no cable clamps in the box.
Thank you for your help.
MartinD is offline   Reply With Quote
Old 01-26-2010, 09:20 AM   #2
What wire are you using ?
12-3 has red/black/white & ground
20.25 (3) #12/3 BX = 13.5 (9 x 2.25) 3 current carrying per wire
13.5 (2) #12/3 NM = 9.0 (6 x 2.25) 3 current carrying per wire
18 (4) Dimmer Switches = 9.0 (8 x 2.25) count as (2) each
2.25
54 total from what I can see
Old 01-26-2010, 09:26 AM   #3
The 12/3 includes the ground. The BX is BLK//WHT/GRN and the NM is BLK/RED/GND. Yes, I forgot to count each switch as two (2).
UPDATED:
(4) Dimmer Switches = 18.0 (8 x 2.25)
Total Volume Required = 42.75 (20.75 spare)
Old 01-26-2010, 09:34 AM   #4
CodeEnforcer
HIVOLT's Avatar
Rewards Points: 99
If this is a 4 gand plastic box you cannot use for BX
HIVOLT is offline   Reply With Quote
Old 01-26-2010, 09:36 AM   #5
Licensed Pro
Two #12 conductors plus ground is called 12/2 not 12/3.
Are sure this isn't BLK/WHT/BARE?
The 42.75ci should be correct.
Old 01-26-2010, 09:45 AM   #6
Yes, this is a metal box.
Old 01-26-2010, 09:49 AM   #7
Thank you for the correction.
Yes, you are correct, it is a bare copper wire. Thank you for helping with the terminology.
Thanks again for all your help.
Old 01-26-2010, 12:12 PM   #8
Electrical Contractor
jbfan's Avatar
Rewards Points: 144
On a side note, what is the load going to be on the dimmers?
4 600 watt dimmers in a single box must be derated, and I'm guessing to 300 watts each or less.
Old 01-26-2010, 03:10 PM   #9
Derated? Could you elaborate?
Dimmer #1: 600W (300W = 4 x 75W)
Dimmer #2: 600W (150W = 2 x 75W)
Dimmer #3: 1000W (600W = 8 x 75W)
3-Speed Fan Switch: 3A (2.5A = 2 x 1.25A)
Could please reference the NEC spec that you are referring to?
Old 01-26-2010, 04:08 PM   #10
CodeEnforcer
HIVOLT's Avatar
Rewards Points: 99
Actually it is not in the code. It is the manufacturers tech specs.
www.lutron.com
Old 01-26-2010, 07:58 PM   #11
Licensed Pro
When you place multiple dimmers in a ganged box, you have to break off cooling fins on one or both sides. When you do that, it reduces the wattage rating of the dimmer.
Slow toilet tank fill even with NEW fill valve? Zilla Plumbing 8 08-10-2009 10:37 PM
Need help with conduit fill calculations kornbln Electrical 6 07-28-2009 01:22 PM
Would you spring to fill in your backyard? Piedmont Landscaping & Lawn Care 4 05-14-2009 09:14 PM
Building a shed, need help with pouring slab / fill ssybert Building & Construction 5 06-12-2008 07:19 AM
2x100a sub on service main jambud Electrical 17 03-12-2008 10:31 AM