-   -   Box Fill Calculation (http://www.diychatroom.com/f18/box-fill-calculation-27417/)
SS396 09-27-2008 09:18 AM
Hi.. I wanted to install a gfci into a one gang outlet box. Cables exiting the box would include a single bx 12/2 , and 2 ea nm12/2. If I understand the box fill calculation, it would be:
2.25 X 6 = 13.5 conductors exiting box
2.25 + 1 = 2.25 grounding conductor
2.25 X 2 = 4.5 gfci
2.25 X 1 = 2.25 clamps
total 22.5
The outlet box installed is 20 in3. and would seem to have plenty of room, but calculates to be smaller than required? Am I doing this correctly? Would this fail an inspection?
DangerMouse 09-27-2008 09:39 AM
i'm using Carlon 22" boxes with no problems. not sure what inspector would say in your case, but others here will. however, are you saying you are putting one live line in, and 5 out, hence 6 wires? i'm not understanding, but what do i know? i'm just a cartoon mouse......
DM
SS396 09-27-2008 09:54 AM
Stated another way, one nm12/2 home run into the box. wires exiting the box are one nm12/2 from load side of gfci to down stream protected outlet and another bx12/2 to a lighting circuit.
Stubbie 09-27-2008 10:05 AM
2.25 X 2 = 4.5 gfci
total 22.5
Is the clamp internal to the box?... ie ...part of the box construction? If it is then you are overfilled. If not you just squeak by...well close enough I wouldn't worry about it.
SS396 09-27-2008 10:34 AM
Thank you both. I guess then that you agree that I am adding up the box fill properly. (Actually, I was hoping that I was doing it wrong.) Seems like the
enclosures are made just a little too small for what seems like a reasonable usage. ie If you have a metal box with internal clamps you are limited to one 12/2 in and one 12/2 out. period.
Pudge565 09-27-2008 10:40 AM
Ok here is how it is done each current carring conductor counts as one wire. So 3 "hots" and 3 neutral is 6. Then you count all grounds as 1. So 3 grounds equals 1 conductor. so we are at 7. plus the device counts as 2 so you are then at 9. And if there is an internal cable clap it counts as one per clamp so it would take you to 12. According to code you would have either 9 or 12 wires depending if you have the internal cable clamps. A B120 meaning a single gang box 20 in3 can hold I think 10 number 12 wires but I am not sure off hand. It should be stamped on the inside of the box most times it will be I will get back to you on how many it can hold though when I find it.
chris75 09-27-2008 06:53 PM
Originally Posted by Pudge565 (Post 161604)
Ok here is how it is done each current carring conductor counts as one wire. So 3 "hots" and 3 neutral is 6. Then you count all grounds as 1. So 3 grounds equals 1 conductor. so we are at 7. plus the device counts as 2 so you are then at 9. And if there is an internal cable clap it counts as one per clamp so it would take you to 12. According to code you would have either 9 or 12 wires depending if you have the internal cable clamps. A B120 box single gang 20 in3 can hold I think 10 number 12 wires but I am not sure off hand. It should be stamped on the inside of the box most times it will be I will get back to you on how many it can hold though when I find it.
What the heck are you talking about? :no:
Pudge565 09-27-2008 07:10 PM
Sorry I did not realize he was talking about calulating out the required volume. However this is a way to get box fill only when using all the same size conductors. Notice how most plastic boxes list how many of certain conductor sizes are allowed in that box this is why.
Stubbie 09-27-2008 09:13 PM
Pudge
Your still calculating incorrectly whether same or different size conductors.
chris75 09-27-2008 09:30 PM
Pudge, check out Art. 314 on box fill.
williswires 09-27-2008 09:56 PM
The required box fill volume was counted correctly by SS396 if the box used is a plastic box with clamps that are internal, or a metal box with the clamping mechanism inside the box. If a box is used that has the clamping mechanism(s) outside the box, such as a Romex connector with a locknut, the clamps are not counted.
Sortof misleading. Each conductor that originates outside the box and is spliced or terminates inside the box, and any conductor which goes through the box without splice, is counted once. However, a conductor which has no part which leaves the box is not counted. For example, a jumper wire from one receptacle to a second receptacle in the same box (like a hot conductor) is not counted. Neither is a pigtail from a switch or receptacle to a splice. I believe these should be counted, but the code specifically excludes them from the count.
Correct.
All clamps together count as one, not one each. Total is 10 so far.
So we now have 9 or 10, depending on the clamps.
The Carlon B120 has an internal volume of 20 cu in. It is molded with allowable fill numbers of 9 for #12, 10 for #14. Nine #12 allowances would add up to 20.25 cu in required, ten #12 allowances would add up to 22.5 cu in required.
If using the info molded into a Carlon blue box, Carlon's position on the clamps is that the UL box fill calculations are with the clamps removed. Therefore, presently the clamp allowance should be deducted from the number of conductors listed on their boxes when using the box So... if a B120 is used, w/ nine #12 conductors marked on it, we have:
9-1 clamp allowance leaves 8 allowances left.
but...we need 6 (hots & neutrals) + 1 (grounds) + 2 (single device yoke) = 9 allowances more
So there we have it, folks. By the required volume calculation method (which is really the only correct one per the NEC), the volume required is 22.5 cu in. unless the clamps are outside the box. By the "use the numbers on the Carlon boxes" method, we are still 1 allowance overfilled.
Either way, the box is too small, but like Stubby said, it's just a little bit. At least you're looking at box fill requirements - some of the posts have demonstrated box fills way overfilled, like 30 cu in required but stuffed into a 20 or 22.5 cu in box!
theatretch85 09-28-2008 03:46 AM
Personally I prefer using 4" junction boxes with a 1 or 2 gang mudring. Generally have more than enough space in the box to do all the wiring needed. If its going to be a 2 device switch box, I usually go with the deep j-box in the event a dimmer needs to be installed; plus the metal box acts as a decent heat sink for the dimmers (better than a plastic box anyway).
chris75 09-28-2008 09:04 AM
Actually it does nothing as far as improvment, the heat is displaced towards the front so the box really does nothing. Besides that, if you dont overload the switches its never a problem anyhow.
Pudge565 09-28-2008 08:14 PM
Correct.
Thank you chris left me hanging as to why I was counting wrong this was very informative.
williswires 09-29-2008 10:09 AM
Chris probably just wanted you to be familiar with looking it up in the code book for yourself instead of explaining the concern right away. That's always the best way...
Hey, at least I gave you 30 mins before I spoiled the fun!:whistling2: