Am I suppose to use this bonding screw? The paper work said "when required". Would it be ok to go ahead and use it? Thanks
Nitwit is offline   Reply With Quote
Old 08-29-2010, 10:15 AM   #2
Electrical Contractor
kbsparky's Avatar
IF this is a service panel, then the bonding screw is required. If this is a sub-panel, then you don't use the bonding screw ... a separate equipment grounding bar is required.
I am more concerned with the use of a 60 Amp breaker on what appears to be a #10 conductor. Unless that is connected to a rather large A/C unit with similar specs on the nameplate, that would be a major code violation.
What is that 100 Amp breaker for? There are no wires connected to it. Is that for the incoming service from a meter box?
Edit to add: After looking at this again, it looks like a generator transfer switch panel? If that #10 is fed from a generator with proper overcurrent protection, then the 60 Amp breaker is fine. I would not use the bonding screw if this is the case.
-KB
Old 08-29-2010, 10:36 AM   #3
Nitwit's Avatar
Thanks for the reply.
Yes, it is a transfer switch for a generator. Thanks for clearing this up for me.
Old 08-29-2010, 01:10 PM   #4
joed's Avatar
Rewards Points: 12,028
If you are not using the bonding screw then you need to move that ground wire to a separate ground bus attached to the metal box.
Old 08-29-2010, 03:11 PM   #5
Nitwit's Avatar
That explains it. I'll add the screw. I just finished wiring it all up and all is well.
Old 08-29-2010, 03:30 PM   #6
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
you can only insert the screw if this is your service disconnect. If it isn't, you do not install the bonding screw.
Is this the first disconnect in your system?
Old 08-29-2010, 03:33 PM   #7
Nitwit's Avatar
Yes it is the first.
Old 08-29-2010, 04:03 PM   #8
nap
You talking to me?
nap's Avatar
then yes, you would run the screw down.
also, if there is such a bonding screw in your breaker panel, you need to remove it and separate all of the grounds and neutrals. The neutrals must be isolated from the ground (electrically) at that panel. You would need to run 4 conductors from this transfer panel to the breaker panel as well.
edit to add:
you also must bring your grounding electrode system to this box and disconnect it from the breaker panel.
Old 08-29-2010, 04:18 PM   #9
Licensed electrician
Rewards Points: 1,296
Those black and red wires do not look anywhere near large enough for the 60 amp breaker they are connected to.
Old 08-29-2010, 04:40 PM   #10
nap
You talking to me?
nap's Avatar
somebody suggest before they might be protected at the generator properly. If so, the 60 amp rating becomes meaningless as they simply become a disconnect.
Obviously, if there is not proper protection at the generator, then yes, those wires are too small for the breaker.
Old 08-29-2010, 06:11 PM   #11
Nitwit's Avatar
The 10 gage wires are protected at the generator.
Stuck Screw IceTreay General DIY Discussions 11 09-09-2010 02:56 PM
Azek Decking and Cortex Screw System EdtheC Flooring 2 08-27-2010 08:48 PM
Swapping old 3ways with new (different screw color configuration on new switch) Michblaze02 Electrical 10 11-08-2009 03:17 PM
Can't get set screw in TP holder loose janralix Plumbing 4 08-12-2009 11:47 PM
Which bonding method proper??? Nestor Electrical 2 09-15-2006 07:18 AM