-   -   Bonding Electrical Panel (http://www.diychatroom.com/f18/bonding-electrical-panel-161298/)
folkda 10-27-2012 09:45 AM
1 Attachment(s)
My first post.
If you look at he attached picture. The home inspector saw that my panel needed bonding screws.
This is a SquareD panel installed in 1979.
I fixed the double tapped Neutrals.
This panel has an exact sister to it right next to this one.
I think this is the First and Main panel Because a Home Inspector only indicated this box was missing bonding screws.
- With that said.
Look at the Neutral Bar - All three bars are connected with a thick steel plate so no neutral or ground could be isolated....
Either way I have been looking up bonding and haven't got a real understanding. On placed looked like you only bond the main box. But the schematic showed the Neutral bonding bar in a sub-panel as isolated see the attached URL
http://www.diychatroom.com/attachmen...l-detached.jpg
To take a stab at it...
The bonding screw makes contact with the Panel Box Thus grounding it...
---Tangent question I don't understand what the big deal is... Ground/Neutral is Ground/Neutral no matter if you are in a Main or sub box... (Okay lay into me)..
First Question - Do I really need the bonding screw in my panel.
Sub Question - Can you point me to the reasoning to bond or not to bond?
Julius793 10-27-2012 11:58 AM
The panel enclosure itself always needs to be bonded to ground simply in case a hot conductor touches it. That applies to all panels!! As to bond grounds and neutrals that only is allowed once at the main panel.
kbsparky 10-27-2012 12:02 PM
Only one of those holes is needed for the box bonding screw, IF this is a service panel.
Service panel, by definition would be the first disconnect after the meter box. You said there was another panel next to this one. Does one feed-thru to the other? Or, are they both fed directly from the outside meter box?
An alternative to installing a bonding screw would be to install a grounding lug and bonding jumper wire from the neutral bar to the enclosure can.
hidden1 11-02-2012 11:37 PM
152 Attachment(s)
Attachment 59948looks similar to mine-trying to locate my bonding screw .did these older square d get installed with a different set up(nothing there at the open spot?)