Bonding An Aboveground Pool - Electrical - DIY Chatroom Home Improvement Forum
Old 08-06-2009, 09:16 PM   #1
Bonding an aboveground pool
My pool is semi-inground. I know now that it should be bonded. Do I need to dig down all around the pool and attach the #8 copper wire at the base or can I attach it at the top of each post under the caps and string it around that way?
MichaelJohn is offline   Reply With Quote
Old 08-07-2009, 01:53 PM   #2
Rewards Points: 128
Not knowing much about above ground pools, I can at least answer your specific question. The bonding grid must be in contact with the earth. It would serve no purpose if it where installed as you intend. The pump motor, the water itself and any metal parts such as ladders must be bonded also. It also must be GFCI protected.
There are others here that will be more specific and know much more. Just keep checking back. Someone will find something wrong with what I said for sure. Then you will get all the answers you need.
I am not even sure you are required to have a bonding grid on an above ground pool. So I will be watching too.
Old 08-07-2009, 02:00 PM   #3
Rewards Points: 1,578
Try:
http://www.selfhelpandmore.com/home-...pools-2002.php
Note: This states based on 2002 NEC so it is dated but may give you an idea of some key concepts. You should check your local town to see what code you have to follow; it is very important for saving lives that you do this properly and according to current guidelines.
bob22 is offline   Reply With Quote
Old 08-07-2009, 03:29 PM   #4
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Assuming the pool is steel (metal sides) and those sides are bolted to each metal post most local codes only require that you bond to no more than 4 of those posts or to the metal bottom track. Your bonding metal around the pool together not dirt so anywhere on that metal post is fine. Just get a bonding/ground lug and put it on the post and attach your #8 copper bonding wire to it. Remember all metal within 5 feet of the pool walls needs to be bonded so you really need to do your homework before you call it a day.
In 2008 minimum safety requirements by the nec have included bonding the pool water. So to do this you attach a bonding widget to the front of your pool motor then start your number #8 bonding wire there then catch the bonding lug on the pump then go on to the bottom track of the pool... bond everything else to the pool bottom track or steel posts. You must also have a grid around the pool perimeter walking area. If the pool is already erected a alternate means to have a grid around the pool is as follows
(b) Alternate Means. Equipotential bonding conductor meeting the following:
(1) 8 AWG bare solid copper bonding conductor.
(2) The bonding conductor shall follow the contour of the perimeter surface.
(3) Use only Listed splicing devices.
(4) Bonding conductor shall be 18 to 24 in. from the inside walls of the pool.
(5) Bonding conductor shall be secured within or under the perimeter surface 4 to 6 in. below the subgrade.
Bonding widget...not the only way but one of the complaint methods
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 08-08-2009, 10:55 AM   #5
Rewards Points: 128
Glad you showed up Stubbie.
Old 08-08-2009, 11:44 AM   #6
When you're done, check that the voltage between the water and all nearby concrete/metal is less than 0.5 vac.
If this voltage is due to phantom voltages, it's less dangerous but you have a problem with improper bonding.
If it's not due to phantom voltages you still have a problem and it's more dangerous.
0.1 vac is probably a reasonable goal.
Tags
bonding , pool , semi-inground
Bonding for Pool Equipment Elecman Electrical 9 03-23-2010 03:09 AM
Another Pool Bonding Question RustyRealtor Electrical 4 08-05-2009 01:15 PM
pool bonding question.? pjwinstalls Electrical 5 06-28-2009 01:32 AM
Wire size for 300watt trans, 3 way 100ft Al the Diy guy Electrical 16 03-22-2008 08:46 PM