-   -   Bathroom Wiring Project (http://www.diychatroom.com/f18/bathroom-wiring-project-56220/)
diyrick28 10-29-2009 04:11 PM
Hoping someone can help me understand what I did wrong.
I am wiring a bathroom with all 12-2 wire and it is all on one circuit 20amp. I have a 3-gang box with sw1 controlling the overhead lights, sw2 the two vanity lights and sw 3 an exhaust fan with no light. also in the bath are two gfi's. I ran the wire from the panel into a junction box where it connects with wires from the overhead lights, vanity lights exhaust fan and gfi's. out of the junction box is one line into the 3 gang which then pigtails to the three switches. Can this work? If so how, If not, what is the easiest way to fix my mess?
jerryh3 10-29-2009 04:16 PM
You should have just went breaker->gfci1->gfci2->switch box->lights/fan.
diyrick28 10-29-2009 04:25 PM
Jerry:
So run the 12-2 from the breaker to the 1st GFI. connect the 2nd via the loads into the hots. Then run 12-2 from the load to the switch box and pig tail off that?
jerryh3 10-29-2009 04:43 PM
As long as this circuit only supplies this bathroom(and no fastened loads over 10A) you can do this. Gfci2 will connect to the line side of the gfci1. You'll connect the feed from gfci2 to the switches to the "load" terminals of gfci2. Pigtail the feeder to your three switches and run 12/2 to each device(overhead,vanity, fan). Get a deep switch box. All of that 12 gauge isn't going to be fun in a standard depth.
jbfan 10-29-2009 04:58 PM
Lights are not required to be gfci protected. The way I would do it is use the line side of each gfci and not the load side.
jerryh3 10-29-2009 05:20 PM
I know they're not required, but I like the protection. Ever find yourself turning on the exhaust fan from inside the shower?
joed 10-29-2009 05:37 PM
The lines to the lights and fan should go to the 3 gang switch box not the 'junction box' with the power. Where is this 'junction box'? Is it one of the GFCI boxes? It can't be buried inside a wall. It has to remain accessible.
rselectric1 10-29-2009 05:38 PM
I agree. In fact, one "authority having jurisdiction" where I have done work requires it. It is included in their local amendments to the NEC with regard to their area.