Bathroom/wet Bar Dual 20/20 - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 02-10-2013, 03:15 PM   #16
MarginallyQualified
Rewards Points: 2,464
Originally Posted by Stubbie View Post
Bathroom receptacles must be 20 amp if your talking about the bathroom.
As I'm reading it... the bathroom is part of the new wet bar work.
But if not... then deal with them when you do the wet bar.
As I'm reading it... the OP will probably need a sub panel for the breaker space all this added on wet bar features (will chew up and is/was hoping to get away with just using tandems).
Whether they meet code or not... I just don't like 'em. Or MWBC's.
I'll repeat: Avoid them both.
Old 02-10-2013, 03:33 PM   #17
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
He has three open spaces that all take tandems. He needs two circuits. Why will he need a subpanel?
Old 02-10-2013, 03:33 PM   #18
Rewards Points: 16
There is nothing wrong with using a tandem breaker to get two 20 amp 120 volt circuits to the bathroom and wet bar. Be sure what you use is indeed a tandem breaker and not a double pole breaker. A tandem will fit in one space with two toggles that are not handle tied. Like so .. cannot use this with mwbc as eastcoastsparky has pointed out. You can also buy them 15/20 instead of both the same
Thanks I am going to use a two pole unit
jiarchibald is offline   Reply With Quote
Old 02-10-2013, 03:34 PM   #19
k_buz's Avatar
That is a tandem breaker not a two pole.
Old 02-10-2013, 03:35 PM   #20
Rewards Points: 16
I agree
Old 02-10-2013, 03:37 PM   #21
Rewards Points: 16
K_Buzz, the breaker in the above photo is the one I have purchased. I was hoping to use this to run two 20amp circuits
Old 02-10-2013, 03:38 PM   #22
eastcoastsparky's Avatar
Rewards Points: 150
So u want a mwbc?
eastcoastsparky is offline   Reply With Quote
Old 02-10-2013, 03:38 PM   #23
Rewards Points: 150
Ok so you will run 2 sets off 12/2 not 12/3 which wiuld be a mwbc
Old 02-10-2013, 03:39 PM   #24
MarginallyQualified
You're right. I missed the space detail and was reading more into it.
Probably your influence from that other thread.
Originally Posted by TheOP
...and two 20 amp plugs below counter to run a mini fridge and wine fridge.
Two circuits total new.
The lights should be just fine being fed off the existing 15A circuit
and the existing basement receptacle 20A circuit (that he still has to find and split up) should be fine for the GP receptacles.
Still though... no tandem needed (or wanted by me).
Old 02-10-2013, 03:39 PM   #25
k_buz's Avatar
You can. However, you cannot run 12/3 to feed those two circuits. You will need to run two separate 12/2's.
Old 02-10-2013, 03:41 PM   #26
Rewards Points: 16
yes 2 new wired with 12-2 from a 20/20 two pole unit shown in the photo posted
all the lights and receptacles, excluding bath and wet bar, will be run on the existing 15 amp
Old 02-10-2013, 03:44 PM   #27
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
I understand what your saying but the fact is .. it's a bathroom and has nothing to do with being part of a wet bar addition. The other fact is he has 3 full size slots available which are rated for tandems which would allow him to have 6 .. 120 volt branch circuits. Why would you want to run a subpanel ... that's my opinion .. He also has square d breakers which allow two wires under a terminal, often this is a good option if loads aren't going to be like those of hair dryers etc...
EDIT ... Sorry i am such a slow typer I didn't see you have already resolved this issue with K buz ...
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 02-10-2013, 03:49 PM   #28
UAW SKILLED TRADES
Stubbie's Avatar
Please stop calling it a two pole breaker it is a single pole breaker with two toggles for two seperate 20 amp 120 volt branch circuits.... Your driving me nuts .....
Stubbie
Old 02-10-2013, 03:54 PM   #29
Rewards Points: 16
I don't think I'll need any 12-3 between any thing being wired on the 20 amp.
for the bath, I was thinking of running 12-2 to a 20amp GFCI receptacle. then to the light switch (using pigtails for continuous flow). then to the fan switch (single) to the fan.
For the wet bar Run 12-2 to the 2-20 amp receptacles below counter With Pig tails, to the 2 20-amp GFCI recept. above counter on either side of sink
whatcha all think?
Old 02-10-2013, 03:57 PM   #30
Rewards Points: 16
Sorry about that. It sates right on the breaker that it is a HACR type 2 pole unit j969.
Thats why I referred to it as that
old dual pane vs modern dual pane DIYGST Windows and Doors 2 12-05-2012 11:14 AM
Dual Stage Furnace grod777 HVAC 34 11-05-2011 10:28 AM
NM cable and Dual fuel range edge130 Electrical 0 11-02-2011 03:48 PM
Dual Cap 35/25MDF 440VAC JJboy HVAC 20 10-10-2011 09:12 PM
Dual Pane Windows No Low E Glass and No Argon Gas Filling AZSun Windows and Doors 4 08-12-2011 09:10 PM