I have a semi finished basement with full bath and a wet bar previously plumed. Both areas share and adjacent wall. I need to add an exhaust fan to the bathroom and I'm planning on adding two 20 amp GFCI plugs on either side of the sink in wet bar and two 20 amp plugs below counter to run a mini fridge and wine fridge. Both rooms and the rest of the basement (lights, outlets, etc.) are on a single 15 amp breaker.
My plan is to run a dual 20/20 tandem circuit from the main panel to the bath and wet bar. leaving the rest of the basement on the 15 amp circuit. the panel is a 200 amp service with room for 3 more breakers. I wanted to save room by using the 20/20 tandem.
My question is, can I do this safely and is this going to bite me in the as* if and when inspections come through.
My understanding of the 20/20 tandem, is that I can run two 20 amp circuits from one breaker. Is this correct?
with this set up if anything trips both the bath and wet bar will go together, is this correct?
jiarchibald is offline   Reply With Quote
Old 02-10-2013, 01:34 PM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
You can only install tandems in a panel rated to take tandem breakers.
If you can install tandem breakers, then each "side" of the tandem will work independently of each other.
Old 02-10-2013, 01:46 PM   #3
Rewards Points: 16
The three open spots can take tandem breakers
Old 02-10-2013, 02:00 PM   #4
Rewards Points: 506
Send a message via AIM to theatretch85
You will have to run separate 12/2 for each circuit from the panel, you cannot use 12/3 to get the two circuits near the bathroom/wetbar area as you would overload the neutral.
theatretch85 is offline   Reply With Quote
Old 02-10-2013, 02:35 PM   #5
eastcoastsparky's Avatar
Rewards Points: 150
He could only run 12/3 if it was a mwbc with a 2 pole breaker
eastcoastsparky is offline   Reply With Quote
Old 02-10-2013, 02:45 PM   #6
MarginallyQualified
Rewards Points: 2,464
Both areas share an adjacent wall.
I need to add an exhaust fan to the bathroom...
Do you already have lighting in that room?
How many other lights in total?
How many receptacles in total?
Old 02-10-2013, 03:04 PM   #7
Rewards Points: 16
I will be running 12-2 to both bath an wet bar.
Old 02-10-2013, 03:12 PM   #8
Rewards Points: 16
There is one light in bath. Wet bar is open to the rest of the basement so no additional lighting needed.
Not including bath, there will be 12 lights and 10 receptacles on existing 15 amp. 4 lights on single-dimmer and 4 on 3-way w/dimmer. One deck light/ single. And three in stairwell. All three in stair well are on 3-way.
Old 02-10-2013, 03:31 PM   #9
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
I think he was explaining that if the OP was thinking mwbc he could not use a tandem breaker.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 02-10-2013, 03:41 PM   #10
UAW SKILLED TRADES
Stubbie's Avatar
As long as the receptacles in the bathroom are on a 20 amp circuit and gfci protected your good. the receptacle circuit cannot extend out of that single bathroom or hiot any receptacles before the bathroom. Also any receptacles close to a wet bar sink need gfci protection if they serve the countertop. Close meaning this ....
210.8(A)(7) Wet bar sinks
Receptacles installed within 6 feet (1.8 m) of a wet bar sink must be GFCI protected where installed to serve the countertop surfaces. The six foot distance is measured from the outside edge of the sink. Receptacles more than 6 feet (1.8 m) from the sinkís outside edge are not required to be GFCI protected. Receptacles not serving the wet barís countertop surface do not require GFCI protection, even if they are within 6 feet (1.8 m) of the sink.
Stubbie
Old 02-10-2013, 03:43 PM   #11
MarginallyQualified
There is one light in bath. Not including bath, there will be 12 lights
and 10 receptacles on the existing 15 amp.
The remedy I'd suggest is to split the existing lights and receptacles.
I suspect that will be easy since the R's were probably added to the lighting circuit.
Keep the 15A for lights (as is) and add the bathroom fan to that.
Provide another (new circuit) for the existing receptacles.
Make it 15 or 20 depending on what wire is used for them.
eta: the original basement plan SHOULD have had at least one 20Amp recep.
Look around for what was provided then and what you have now.
When you're able to sort that out... be sure about the wire used.
The remodel work, wet bar outlets and appliances, will need what they need.
Avoid using tandem breakers or MWBC's when you do that.
If you have a shortage of breaker space... fix that.
Old 02-10-2013, 03:45 PM   #12
UAW SKILLED TRADES
Stubbie's Avatar
I suspect that will be easy since the R's were probably added to the lighting circuit. Keep the 15A for lights (as is) and add the bathroom fan to that.
Make it 15 or 20 depending on what wire is used on them.
Bathroom receptacles must be 20 amp if your talking about the bathroom.
Stubbie
Old 02-10-2013, 03:48 PM   #13
Rewards Points: 16
I'm trying to run two 20 amp circuits off one 20/20 breaker. mainly because the exhaust in bath and the separate wet bar circuit. I could run just a 20 amp to both fan and wet bar, but with the the rest of the basement on a 15 amp service. I'd like to lighten the load especially with an entertainment section (TV, Music, etc.)
I do have to room for 2 20/amp just thought I'd save space with the tandem
So, I'm guessing I need to return my 20/20 tandem and pick up two 20/amp breakers and run both bath and wet bar on separate breakers.
Old 02-10-2013, 03:52 PM   #14
Rewards Points: 150
I'm not sure what you gents are referring to with MWBC
(main wet bar circuit?) but I'm trying to run two 20 amp circuits off one 20/20 breaker. mainly because the exhaust in bath and the separate wet bar circuit. I could run just a 20 amp to both fan and wet bar, but with the the rest of the basement on a 15 amp service. I'd like to lighten the load especially with an entertainment section (TV, Music, etc.)
Mwbc- multi wire branch circuit. Using a double pole breaker with only one nuetral if one circuit were to trip they both would bc they are handle tied together
The Following User Says Thank You to eastcoastsparky For This Useful Post:
jiarchibald (02-10-2013)
Old 02-10-2013, 04:15 PM   #15
UAW SKILLED TRADES
Stubbie's Avatar
There is nothing wrong with using a tandem breaker to get two 20 amp 120 volt circuits to the bathroom and wet bar. Be sure what you use is indeed a tandem breaker and not a double pole breaker. A tandem will fit in one space with two toggles that are not handle tied. Like so .. cannot use this with mwbc as eastcoastsparky has pointed out. You can also buy them 15/20 instead of both the same
Stubbie
old dual pane vs modern dual pane DIYGST Windows and Doors 2 12-05-2012 12:14 PM
Dual Stage Furnace grod777 HVAC 34 11-05-2011 11:28 AM
NM cable and Dual fuel range edge130 Electrical 0 11-02-2011 04:48 PM
Dual Cap 35/25MDF 440VAC JJboy HVAC 20 10-10-2011 10:12 PM
Dual Pane Windows No Low E Glass and No Argon Gas Filling AZSun Windows and Doors 4 08-12-2011 10:10 PM