Bathroom Exhaust Fan, Need Separate Circuit? - Electrical - DIY Chatroom Home Improvement Forum
Old 04-15-2011, 11:26 AM   #1
bathroom exhaust fan, need separate circuit?
I'm installing an ehaust fan in one of our bathrooms. The fan say it can be installed in the shower enclosure as long as it is GFCI protected. Can I simply add a GFCI outlet and run from it the feed to the fan thereby giving it GFCI protection? Also do I need a separate circuit for the fan? Thanks for your help.
beech is offline   Reply With Quote
Old 04-15-2011, 12:03 PM   #2
Scared Electrician
Saturday Cowboy's Avatar
how much current does the fan pull?
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
Old 04-15-2011, 12:41 PM   #3
joed's Avatar
Rewards Points: 12,852
If you have an existing GFCI circuit you can use it.
If you are running a new GFCI circuit then it needs to be 20 amp if it is in the bathroom. You can connect your fan to the LOAD terminals.
Old 04-15-2011, 01:03 PM   #4
Can the existing GFCI circuit be 15 amps and still OK to run the fan off it? Thanks
Old 04-15-2011, 01:04 PM   #5
TY Saturday cowboy. Draws 1.0 amps
Old 04-15-2011, 05:21 PM   #6
Scared Electrician
thats a good question, I'm not rightly sure. Being that it is old installation it is grandfathered in so the new code does not matter. But adding anything to anywhere at any time requires it to be installed to the newest applicable code. That said i'm gonna go with NO. Maybe somebody else will chime in and confirm.
the current requirements are not a problem.
The Following User Says Thank You to Saturday Cowboy For This Useful Post:
beech (04-15-2011)
Old 04-15-2011, 06:00 PM   #7
I'm not sure about a 15A circuit but with a 20A circuit (if you have only 1 bathroom on this circuit) can feed receptacles, lights, and equipment within the bathroom.
Anything not fastened must not exceed 80% of the circuit rating (16A). Anything fastened in place, which would be the fan, correct? Would need to be less than 50% of the circuit (10A).
If you come to the conclusion you may need a new circuit for the fan and only have 1 bathroom on this branch circuit - look into upgrading this circuit to a 20A.
FutureSparky is offline   Reply With Quote
The Following User Says Thank You to FutureSparky For This Useful Post:
beech (04-15-2011)
Can bathroom exhaust and dryer share same outside duct? benze HVAC 17 09-08-2010 02:24 PM
bathroom receptacle circuit Steve Burke Electrical 7 07-15-2010 07:37 PM
Condo Bathroom exhaust fan schnitz411 HVAC 0 05-26-2010 04:59 PM
Bathroom exhaust... the ongoing saga... landev HVAC 9 01-05-2009 07:49 PM
Bathroom circuit ptcamaro Electrical 3 04-21-2008 07:44 AM