I am running the cables through my unfinished basement wall and I have two simple questions...
1. The book I have says that the cable must be stapled within 8 inches of the box. Is it ok if I do it closer than that, say 4 inches? Or should I shoot for 8?
2. The book also says to run the cables 20 inches above the floor. Is this a code or just general practice? Is there a range, for example 20 inches +/- 6 inches?
epeterson777 is offline   Reply With Quote
Old 02-06-2009, 07:57 PM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
Actually it's within 12" of the box, etc. So as long as you got that ,you're good.
Don't know about the other, unless it's a moisture thing. I'm usually higher than that so I don't have to bend to run the wire.
wirenut1110 is offline   Reply With Quote
Old 02-06-2009, 07:59 PM   #3
Licensed Pro
It's 8 inches for single gang plastic boxes.
Old 02-06-2009, 08:08 PM   #4
Rewards Points: 510
Is that new? 2008?
Old 02-06-2009, 09:42 PM   #5
"The Book" ? What book ?
I use my hammer, put it in the stud bay, put outlet box on top, nail in place. For old construction I match what's in the room. In the basement mine will be approx 4' off the floor in case of a flood
Basement will be unfinished, so I'd rather have them up off the floor
Old 02-06-2009, 10:00 PM   #6
remodeling pro
I'm not a licensed electrician, but 8" has always been my understanding.
As for the 20" horizontal run, it has nothing to do with any code to my knowledge, but rather an efficient use of wire. Since most base outlets are set around 16" above the floor, it makes for short, economical drops into the boxes. The hammer handle as a gauge method mentioned is common in the trade, and puts the boxes in this range, provided you don't have an electrician who uses a 28oz Eastwing .
troubleseeker is offline   Reply With Quote
Old 02-06-2009, 10:29 PM   #7
334.30 Within 12" of box
Old 02-06-2009, 10:41 PM   #8
Rewards Points: 77
The book I have been using is the Black and Decker: The Complete Guide to Home Wiring.
Old 02-06-2009, 10:55 PM   #9
Many of these types of books have incorrect information in them
Some have been recalled
Always verify information 1st before proceeding
Old 02-06-2009, 10:56 PM   #10
1. If you are measuring the distance from the box to staple your cables, you are overthinking it.
Boxes with clamps = 12", boxes without = 8" (I think)
Don't staple them at 4". Let the cable come smoothly, straight up from the box to the stud.
2. Running cables below 20" would be a pain in the back to drill and install but you can do it.
220/221 is offline   Reply With Quote
Old 02-06-2009, 11:04 PM   #11
And the code for the measurement you are quoting?
Maybe this differs by the cable, the section of NEC I quoted is for NM
320.30 (B) - same for AC cable type
Old 02-06-2009, 11:11 PM   #12
Electrician
314.17 (C)Nonmetallic Boxes and Conduit Bodies
Exception: Where nonmetallic-sheathed cable or multiconductor Type UF cable is used
with single gang boxes not larger than a nominal size 57 mm 100 mm (2 1/ 4 in. 4 in.)
mounted in walls or ceilings, and where the cable is fastened within 200 mm (8 in.) of the
box measured along the sheath and where the sheath extends through a cable knockout
not less than 6 mm ( 1/ 4 in.), securing the cable to the box shall not be required. Multiple
cable entries shall be permitted in a single cable knockout opening.
chris75 is offline   Reply With Quote
Old 02-06-2009, 11:18 PM   #13
Thanks, I have heard 8", 12" & wanted to know the specifics
Old 02-06-2009, 11:24 PM   #14
Electrician
Your welcome.
Old 02-07-2009, 07:33 AM   #15
All we need now is a multi trade code for hammer length on new construction sites and everything will finally come out level
Chemist1961 is offline   Reply With Quote
Running 6/3 cable-do I need conduit? Kips Electrical 6 01-16-2009 12:36 PM
Basic wood cutting question sharding Carpentry 4 08-02-2008 05:56 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 12:33 PM
running ethernet through attic null_pointer_us Building & Construction 3 05-15-2006 06:08 PM
very basic drywall question Knyte260 Building & Construction 3 07-18-2005 04:09 PM