Is it code to run 4 or 3 500w (240v) baseboard heaters off one 22amp(two pole) rated thermostat on 12/3 romex?
matrix733 is offline   Reply With Quote
Old 02-17-2008, 09:59 PM   #2
Floor Sweeper
Baseboard Heaters
A 20 amp circuit will easily handle 4 heaters of this size. (4x500w=2000w/240v=8.3A) A 15 amp circuit will suffice. Why the 12/3? The heaters are straight 240, so you only need 2 hot wires plus ground. 12/2 will work just fine. Be sure to reidentify the white as a "hot'' conductor.
junkcollector is offline   Reply With Quote
Old 02-17-2008, 10:13 PM   #3
Electrician
Baseboard Heaters
Just a side note fixed electric heat must also be figured at 125%... so,
(4x500w=2000w*125%=2500w/240v=10.41A
chris75 is offline   Reply With Quote
Old 02-17-2008, 11:48 PM   #4
Baseboard Heaters
Thanks, I forgot that I did not need a neutral for the heaters.