Baseboard Heater Circuit Design - Electrical - DIY Chatroom Home Improvement Forum
Old 11-08-2013, 05:03 PM   #1
Rewards Points: 1,062
Question
I am designing the circuit(s) for my basement apartment (cca. 800 sq ft) baseboard heating solution. I am planning to buy Berko HBB Series heaters and distribute them as shown in the below table. All have a voltage of 240/208.
Code:
Location        Model       Length(in.) Watts       Amps
Living Room     HBB1504     70          1500/1125   6.3/5.8
Bath            HBB504      28          500/375     2.1/1.8
Bedroom         HBB1254     58          1250/938    5.2/4.5
Hallway         HBB754      34          750/563     3.1/2.7
My questions are:
1. Should I split them into two circuits (living room and bathroom in one, bedroom and hallway in the other) or is it OK to keep them all on one circuit?
2. Is the voltage a factor in determining the wire gauge? I know that the amperage is. E.g. if I split them in two circuits so that each circuit bears less than 10A each, can I go with AWG 14/3 even though the voltage is double than usual? Or simply put, which AWG should I use for either scenario from question 1.?
I have an extensive experience as a DIY electrician, I have pretty much rewired most of my house and have set up one 240/120 circuit for my dryer (used AWG 10/3). But this is considerably lower amperage so I am not sure what AWG to use.
Old 11-08-2013, 05:43 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 224
Code:
My questions are:
14/2 on a 2 pole 15 amp breaker for each pair of heaters.
I almost would be tempted to put them all on a 20 amp circuit and 12/2 wire.
Old 11-08-2013, 05:50 PM   #3
Doesn't dual voltage require two hots?
Old 11-08-2013, 05:52 PM   #4
Oso954's Avatar
Rewards Points: 740
Warm weather areas can get away with the one circuit.
Cold weather makes 2 circuits much more desirable. One problem won't take out all the heat.
Oso954 is online now   Reply With Quote
Old 11-08-2013, 06:00 PM   #5
Well if I am home, I flip the breaker back on. If I am away, who cares if it is colder?
Old 11-08-2013, 06:31 PM   #6
jbfan's Avatar
Rewards Points: 224
The 240 requires 2 hots, but does not require a neutral.
Old 11-08-2013, 06:41 PM   #7
Hmmm. That sure is interesting. Never seen anything that "does not require a neutral". I trust you but can you please explain this phenomenon so it makes sense to me?
Old 11-08-2013, 06:57 PM   #8
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
I generally use 10 watts per sq. ft. with a 8 ft. ceiling, Thats how I size the required amount of electric heat required, now with that said, using 15 amp breakers you are allowed 11' of electric heat @ 250 watts per ft, and 15' of electric heat at 20 amps, those numbers are the deciding factor when laying out electric heat, I also use heat relays and low voltage t-stats because I like them in my opinion…
you are already over 16 amps, and electric heat is considered a continuous load, you need 2 circuits…..either 15 or 20 amps….
Old 11-08-2013, 06:59 PM   #9
E2 Electrician
Not every appliance requires a grounded conductor (neutral), a electric water heater or AC unit is a perfect example…
Old 11-08-2013, 07:02 PM   #10
E2 Electrician
Impossible, over 80% of a 20 amp circuit…..
Old 11-08-2013, 09:36 PM   #11
MarginallyQualified
Rewards Points: 2,464
Your space (880SF x 7ft ceiling) = 6160 watts total
You don't have enough heaters.
Get another 2000 watts worth.
That (6000/240) is AT LEAST two 20A 240V circuits.
I'd suggest running those circuits through a relay
with a 24V coil... and using a 24V set back thermostat
(and of course a 24V transformer too).
Old 11-08-2013, 09:44 PM   #12
E2 Electrician
They make electric heat relays with built in transformers…..
Old 11-11-2013, 10:59 AM   #13
why would i need a relay? and where would i install it? the elec. panel?
Old 11-11-2013, 11:23 AM   #14
you don't need to run 120 and 240 to the heaters. you can use either voltage.
you don't necessarily need a relay. if you get a thermostat rated for line voltage and the amperage of the circuit, you wouldn't need a separate relay. berko makes line-rated thermostats, check out their website.
itsnotrequired is offline   Reply With Quote
Old 11-11-2013, 04:03 PM   #15
MarginallyQualified
There are more options available with 24V thermostats.
Put the entire space under one control.
The relay will handle the load.
Tags
baseboard heaters , circuit , wire gauge
Baseboard heater questions frohboy33 Electrical 25 02-13-2013 02:01 PM
Want to install a narrow shelf above hot water baseboard heater... nhwoodhobbyist HVAC 8 09-26-2012 06:55 PM
Converting hard-wired baseboard heater to plug Mia Electrical 5 01-02-2010 04:16 PM
wiring a 240V baseboard heater 777 Electrical 10 05-17-2009 11:47 AM
Electric Baseboard Heater Problem goombie Electrical 9 12-23-2008 01:13 AM