Bad Circuit Breaker? - Electrical - DIY Chatroom Home Improvement Forum
Old 11-15-2011, 12:02 PM   #1
Bad Circuit breaker?
I installed a generator interlock in my panel. all circuits work fine on utility power, on generator power I'm only getting voltage on every other circuit. I am assuming the 30amp 2 pole breaker for the interlock is damaged. Any ideas?
mdaigs34 is offline   Reply With Quote
Old 11-15-2011, 12:27 PM   #2
Taking appropriate precautions measure the voltage drop across the switched-on CB. You should not see more than millivolts.
Old 11-15-2011, 12:29 PM   #3
Yeah your missing a phase somewhere. You can determine this using a volt meter and measuring across both legs coming off the generator. If you get 240 coming out of the gen at the point it attaches to the breaker then I would replace the breaker. If you do not get 240 at this point your problem is elsewhere.
Colomboj is offline   Reply With Quote
Old 11-15-2011, 01:31 PM   #4
Licensed electrician
Rewards Points: 1,876
Measuring between a properly fed or wired two pole breaker you should see 240 volts, not millivolts.
Old 11-15-2011, 03:13 PM   #5
should read
Taking appropriate precautions measure the voltage drop across the closed contacts of each pole of the switched-on CB. You should not see more than millivolts.
My bad. It depends on what is meant by 'across.'
Traister wrote a handbook of electrical testing but did not live to see it go to print. IIRC, his numbers were
less than 30 mV for good contacts
and
more than 100 mV for bad contacts.
at rated current.
circuit breaker? blueandyellow Electrical 7 01-30-2011 10:27 PM
Need to ID old circuit breaker box oldfeller Electrical 11 07-26-2010 04:00 PM
A/C unit keeps throwing circuit breaker MofElPaso HVAC 15 05-03-2010 11:06 AM
Circuit BReaker Question - breaker didn't trip and no power thru the circuit Ronin_67 Electrical 2 08-08-2008 06:06 AM
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 05:55 AM