Igorr 11-20-2012 11:22 AM
I have an older house and decided to replace attic lights yesterday. It has the metal boxes and older 2 conductor copper wire with no ground connected to a switch on a different floor.
I am considering two options:
- Installing a GFCI type receptacle at the first box in the feed.
- Providing ground from a nearby box (attic fan) that is grounded properly.
Could you please provide the feedback?
rjniles 11-20-2012 05:03 PM
You can not use a ground from another circuit.
If you are replacing lights on existing ungrounded lighting outlets, you do not have to add a ground.
Igorr 11-20-2012 05:36 PM
rjniles, thank you for the reply!
I am also replacing wires and the boxes. And the new lighting fixture comes with the ground wire.
Installing a GFCI type receptacle at the first box in the feed will do the job, right?
Jim Port 11-20-2012 07:06 PM
A GFI does not provide a ground.
The ground either comes in the circuit wiring or with a metallic raceway.
stickboy1375 11-20-2012 07:07 PM
12 Attachment(s)
Also, you cannot extend an ungrounded circuit...