Arc Fault Trouble Shooting - Electrical - DIY Chatroom Home Improvement Forum
Old 06-13-2007, 04:13 PM   #1
Question
Just wired new home can't get arc fault to work right. When circuit is active breaker trips. If I turn off lights breaker will stay on. But if switch on any over head light breaker trips. Can any one give me some tips on how to trouble shoot this problem.
michael byrnes is offline   Reply With Quote
Old 06-13-2007, 04:25 PM   #2
If it does this no matter which light switch you turn on.
The first thing that I would try is a new arc fault breaker.
They often come bad out of the box.
Master Electrician
jwhite is offline   Reply With Quote
Old 06-13-2007, 04:39 PM   #3
I changed with anouther one from the same box, Should I try a 3ed?
Old 06-13-2007, 05:21 PM   #4
Master Electrician
JohnJ0906's Avatar
If the second one also tripped under the same circumstances, then you have a problem. My guess is that a bare grounding wire is touching a neutral screw in a receptacle. This wouldn't trip the AFCI until a load is applied to the circuit, ie: a light.
Check all your outlets, (POWER OFF! ) look for grounds touching the sides or back of the receptacles.
John from Baltimore
One Day at a Time
"Experience is what you get when you were expecting something else"
"The bitterness of low quality lingers long after the sweetness of low cost is forgotten"
JohnJ0906 is offline   Reply With Quote
Old 06-13-2007, 05:24 PM   #5
Licensed Pro
Also make sure you have the breaker wired correctly. The white wire for that circuit must connect to the silver screw of the breaker and the white pigtail from the breaker goes to the neutral bus.
In-Floor Heating Cable Trouble... sootybuttercup Electrical 24 12-18-2014 09:01 PM
gas heater trouble toughy HVAC 2 11-04-2006 02:55 PM
Trouble - Goodman GMP100-3 Rev B cstelter HVAC 1 10-24-2006 01:27 PM