Arc Fault Breakers Keep Tripping - Electrical - DIY Chatroom Home Improvement Forum
Old 04-07-2012, 11:13 PM   #1
arc fault breakers keep tripping
Working on a small remodel. we were required to add 2 arc fault breakers for the new rooms. as soon as somthing is pluged in it trips the breaker. Same thing on the other circuit. no miss wiring, no shorts, no overload. If i take the wire off and land it on a standerd breaker it will hold a load.
the breakers are on a 150 amp subpanel. is it possible the breakers are picking somthing els up off the main bus and tripping? Its an older home with alot of existing wiring.
Any help would be great
Kenny101 is offline   Reply With Quote
Old 04-07-2012, 11:18 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 386
New circuits or added to exsisting?
jbfan is online now   Reply With Quote
Old 04-07-2012, 11:25 PM   #3
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Are you plugging the same thing in each time? Is, what you are plugging in, turned on when you plug it in? How are the circuits wired? 2 2-wire circuits, or 1 3-wire circuit?
Old 04-07-2012, 11:36 PM   #4
They are new circuits. I have tryed plugging in a couple different things. within a couple seconds it will trip.
Old 04-07-2012, 11:38 PM   #5
k_buz's Avatar
How are the circuits run from the panel? Each with its own neutral, or are they sharing a neutral?
Old 04-07-2012, 11:38 PM   #6
Its pretty basic thats why im confused. It is two 2 wire circuits. they just hit a few receptacles in each room.
Old 04-07-2012, 11:39 PM   #7
k_buz's Avatar
Where did you land the neutrals from those circuits in the panel?
Old 04-07-2012, 11:41 PM   #8
each circuit has its own neutral. I pigtailed each plug...
Old 04-07-2012, 11:41 PM   #9
jbfan's Avatar
Rewards Points: 386
Disconnect the wires after the first receptacle and test.
Some of the basics are
Neutral/ground touching somewhere.
Over driven staples.
Neutral wires not connected to the breakers.
Crossed neutrals in the panel.
Old 04-07-2012, 11:42 PM   #10
k_buz's Avatar
Did you terminate the neutral from those branch circuits to the breaker or the neutral bar?
Old 04-07-2012, 11:42 PM   #11
neutral bus...witch is maxed out by the way. but nothing is doubled up.
Old 04-07-2012, 11:42 PM   #12
neutral bus...
Old 04-07-2012, 11:43 PM   #13
k_buz's Avatar
There's your problem.
The neutral from the branch circuit needs to be landed to the breaker then the white coiled wire off the breaker goes to the neutral bar.
The Following User Says Thank You to k_buz For This Useful Post:
jbfan (04-07-2012)
Old 04-07-2012, 11:45 PM   #14
k_buz's Avatar
I think I should be more specific...there are two different terminals on the breaker (unlike a normal breaker) the front one is for the hot and the back one is for the neutral.
Check the instructions that came with the breaker.
Old 04-07-2012, 11:46 PM   #15
ok thanks. i will swap them over. This is my first time dealing with these breakers. Thanks for the help.
Arc Fault breakers (warning) Potomac101 Electrical 68 01-05-2012 03:22 PM
Arc Fault Tripping JLW74403 Electrical 2 07-25-2011 10:21 PM
Can I install tandem breakers to stop my breakers from tripping? sofakng Electrical 1 04-29-2009 01:44 PM
Subpanels & cutler hammer arc fault breakers MoreCowbell Electrical 13 04-04-2008 10:19 PM
ARC Fault Breakers tripping after a fan install. jAutumna Electrical 32 03-20-2008 08:10 AM