arc fault breaker tripping
I'm trying to install an arc fault breaker but its tripping off any thoughts?
karsat is offline   Reply With Quote
Old 09-13-2011, 07:31 PM   #2
Code05's Avatar
Rewards Points: 1,104
ground to neutral touching or smashed cable.
Code05 is offline   Reply With Quote
Old 09-13-2011, 07:39 PM   #3
what do you mean by ground to neurtral touching?
Old 09-13-2011, 07:50 PM   #4
Code05's Avatar
The wires in a box.
Old 09-13-2011, 08:47 PM   #5
Licensed electrician
Rewards Points: 1,758
Loose connection? Did you wire the circuit neutral to the breaker and the tail to the buss? Is this happening under load or as soon as you turn the breaker on?
Old 09-13-2011, 10:25 PM   #6
As soon as it's connected I don't see any loose connection
Old 09-13-2011, 11:12 PM   #7
dmxtothemax's Avatar
Rewards Points: 5,496
1 - Is it the correct size breaker for the load ?
2 - You have a short circuit somewhere !
3 - Faulty breaker !
What was there before ?
Where there any problems before ?
dmxtothemax is online now   Reply With Quote
Old 09-13-2011, 11:28 PM   #8
1.Yes the breaker is of correct size
2.there was 15 amp regular circuit breaker which was wroking fine
3.this is a new breaker may be its faulty
Old 09-14-2011, 01:31 AM   #9
How is the breaker wired in the panel? With an AFCI or GFCI breaker the hot (black) and neutral (white) leads of the circuit should be connected to the breaker's two terminals, while the coiled neutral lead that came attached to the breaker should be connected to the neutral bus bar. If this is correct on your end, you probably have a fault further along the circuit as suggested by dmx and Code05.
TheAcademician is offline   Reply With Quote
Old 09-14-2011, 10:06 AM   #10
Found the issue
The neutral wire is kind a loose and also now the problem is the neutral wire is short by 2 inches...any alternates other than making a joint ?
Old 09-14-2011, 10:49 AM   #11
Code05's Avatar
What is your problem with a proper splice?
Old 09-14-2011, 10:54 AM   #12
no problem in splicing just wanted to be safe
Old 09-14-2011, 11:09 AM   #13
Code05's Avatar
Proper splices are safe.
Old 09-14-2011, 11:58 AM   #14
Please tell me how to splice electrical wires safely
Old 09-14-2011, 12:21 PM   #15
Code05's Avatar
How about a wire nut. Power off!!!!