Old 07-15-2012, 11:24 PM   #16
Originally Posted by andrew79 View Post
120/208 is for three phase wiring
$#+*"!# Darn it ...........is there any to use this appliance with single phase !
STEVEIEB is offline   Reply With Quote
Old 07-15-2012, 11:31 PM   #17
Master Electrician
120/208 is the three phase wiring 240 is the single phase wiring. It does require a neutral as well though. So as stated previously its 50a under single phase operation and you would need to feed it with a red,black,white number 6 and a number 8 ground(not sure if that's the right ground size for nec). It's probably a direct connect. It will need to be fed off a two pole 50 amp breaker.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
The Following User Says Thank You to andrew79 For This Useful Post:
STEVEIEB (07-16-2012)
Old 07-15-2012, 11:35 PM   #18
" Euro " electrician
frenchelectrican's Avatar
Not always the case due some area they may used 120 - 208 volts single phase as well. ( that is from the three phase network system )
However ., You are in luck anyway it can be reconferated to run single phase as well.
So to use the single phase is not a issue.
Merci,
Marc
Old 07-15-2012, 11:38 PM   #19
Andrew .,
#10 is used for ground up to 60 amp.
Now I will adress to the OP .,
Are you plan to run this in NM or in conduit ? ( where this unit will be located ? )
Merci,
Marc
The Following User Says Thank You to frenchelectrican For This Useful Post:
Old 07-15-2012, 11:48 PM   #20
Master Electrician
Ya its 10 here too, I just looked it up. Didn't know off the top of my head so figured bigger was better :D.
Old 07-16-2012, 07:55 AM   #21
Originally Posted by frenchelectrican View Post
Andrew .,
Merci,
Marc
Thank you for all your helpful info. >>>> the unit will be installed in a pole barn , heated room , not too far from main panel >>>> setting up a small laboratory to do plant tissue culture !
Im going to post more specs from the manufacturers internet site asap>>> hers the link
http://www.mfii.com/images/pdf/Steri...Bs6049a%5D.pdf
Old 07-16-2012, 03:31 PM   #22
Rewards Points: 266
No problem hooking this up to 240 single phase with neutral if it is like the one I used to use. I had this done several years ago, but an EE that works for the company, in a financial capacity, handled all the details with the electrician. (he likes to do that kind of stuff,)
Beware that there are connections that must be change to match the power supply. The EE did this too. There is an internal terminal block where this is altered. IIRC, there is less power available at single phase.
Note that you might need to change the safety valve to get good operation at 15 psi. I recall getting an updated version from the manufacturer, but even that was not high enough pressure. The supplied safety valve is set just to high compared to the safety valve to operate well. I bought one from a local shop (17 psi) and installed it.
ionized is offline   Reply With Quote
Old 07-16-2012, 04:46 PM   #23
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
only have single phase
Yes Marc , I have 240 volts capability to this appliance if required , just a bit more work & wire to do it ......... what is the ( 120 / ) ON THE MODEL # ID TAG for if it absolutely needs 240 V ?
The 120 means there is a 120v load within the unit along with the 240v loads. This is why it calls for single phase 3-wire or 3-phase 4-wire. It means you also need a neutral with the hots.
NO WAY you can hook this unit up to only 120v. Not even close.
The Following User Says Thank You to Speedy Petey For This Useful Post:
frenchelectrican (07-16-2012)
Old 07-16-2012, 05:06 PM   #24
Rewards Points: 266
Oh, you could. It would not be very rational. You'd only be able to get a fraction of the heating capacity so the unit would reach its target very slowly if at all.
Old 07-16-2012, 07:12 PM   #25
Electrical Contractor
kbsparky's Avatar
According to the installation manual, you need a neutral connection.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Old 07-16-2012, 09:13 PM   #26
Master Electrician
The heater will work. Just half as hot. Although it probably won't even turn on without a 120 control circuit and that means a neutral. We're in the business of telling people the right way to do things not the duct tape method.
Old 07-16-2012, 09:49 PM   #27
Ok >>>>>>>>>>> I want 2 do this right ........( no duct tape ) lol......so I'll contact the mfgr. to see if I need to reconfigure the machine inside for handling single phase 220 V . then as stated erlier use the 3 wire method on a 50 amp dedicated circuit ..................
sound right ?
wow >>>>>>am I reading this right ? the nameplate on the unit states it is a 12 kW unit and does this installation instruction show if if it's 12 kW then it going to have to be wired 3 phase ? (see nameplate pic and install instructions )
http://www.mfii.com/images/pdf/Steri...5Bh2115%5D.pdf
*AMP/PHASE
MODEL kW Hz
Single Phase Three Phase
208V 240V 208V 240V
STM-E(L) 9 60 45A 52A - -
STM-E(L) 12 60 - - 26A 30A
Last edited by STEVEIEB; 07-16-2012 at 10:25 PM. Reason: added link 2 mfgr. install instructions
Old 07-16-2012, 10:17 PM   #28
Master Electrician
Yes. You may not have to but most times it will have a multi tap at the electrical connection point. Probably a plate comes off and there will be a diagram on the back that shows what to connect to where for what voltage. Never hurts to check with the manufacturer though.
Old 07-16-2012, 10:27 PM   #29
Old 07-16-2012, 10:38 PM   #30
I'm soooooooo confused...........I definately will be getting someone knowledgeable to help or an electrician to install 4 me
Electricity is so foreign to me......and dangerous ......and this is no cake -walk here on this one !
Tags
appliance
explanation of 220 volt current to appliance Captflx Electrical 2 04-27-2011 05:50 AM
Appliance pigtail manofmany Electrical 4 08-12-2009 11:00 AM
dead-end nipple before a gas appliance amakarevic Plumbing 14 11-02-2008 09:12 AM
CSST gas line through ceiling/floor to appliance pcampbell HVAC 2 05-20-2008 06:36 PM
Issues with appliance plug hgiljr Electrical 1 03-17-2007 07:09 AM