Anyone Know If This Is 3 Phase? - Electrical - DIY Chatroom Home Improvement Forum
Old 07-10-2011, 09:52 PM   #1
www.prosperitees.org
Anyone Know If This is 3 Phase?
I own a screen printing business and we are looking to upgrade some equipment. We need:
1) Compressor - 30 amps single phase 220
2) Dryer #1 - 25 amps single phase 220
3) Dryer #2 - 30 amps single phase 220
And everything else that is run lights, AC, computers etc etc.
As you can see its alot of amps and my building which I lease has a 100 amp main breaker but appears to be 3 poles. Does this translate into 3 phase? I am attaching pictures of the main panel.
Anyone Know If This is 3 Phase?-main-meter.jpg   Anyone Know If This is 3 Phase?-main-breaker.jpg
Prosperi-Tees is offline   Reply With Quote
Old 07-10-2011, 09:58 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,990
Yes, that is 3-phase. You should be fine if the loads are balanced out properly. Your electrician will know exactly what to do.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Prosperi-Tees (07-10-2011)
Old 07-10-2011, 10:01 PM   #3
Wow that was "Speedy"! I appreciate that. That will allow me to look into 3 phase equipment which will allow me to buy larger capacity equipment and be more productive! Thanks
Old 07-10-2011, 10:03 PM   #4
Well, you only asked about the existing equipment. Larger equipment will draw more. 100A is not very much for a place like this. Be careful getting anything bigger.
Old 07-10-2011, 10:09 PM   #5
Well if I got the same equipment in 3 phase instead of single phase I would not have any trouble you think? The 3 phase models of the equipment I am looking at have lower amp requirements especially the infrared dryers.
Old 07-10-2011, 10:32 PM   #6
Electrical Contractor
kbsparky's Avatar
You need to determine whether you have delta-connected or wye 3 phase there.
The difference is the system Voltage:
Delta connected offers you 240 Volts between phases.
Wye service has a nominal system voltage of 208 between phases.
There is no such thing as "220" in the US.
IF you have only 208 Volts, be advised that any equipment that has resistance loads in it will operate at 25% lower capacity. But motor loads will actually require higher Amps to compensate for the lower voltage.
How about posting a picture of the rest of the panel/load center?
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Old 07-10-2011, 10:41 PM   #7
Idiot Emeritus
Rewards Points: 1,492
This is indeed a 3 phase service. There are two types of 3 phase power commonly connected to buildings such as yours; 120/208 wye and 120/240 delta.
It would be good to know which type of power you have.
If it is a 120/208 wye, then your '220' is actually 208. Almost all 220 equipment (single or 3 phase) will run on 208 ok, but heaters will produce 25% less heat. This can be corrected by a buck-boost transformer if needed.
A lot of equipment is marked 208-230 or 208-240. If so, it'll have two amp (or KW) ratings as well. The lower amp rating is almost always for 208.
If the system is 120/240 delta, there will be 240 between any two phases. Two of the phases are 120 to neutral (useful for receptacles, lights and other 120 stuff), the other phase will be 208 to neutral. This 'high leg' is useful for 220 single and 3 phase loads only.
Rob
P.S If you can get the equipment 3 phase, it's better to do so.
micromind is offline   Reply With Quote
The Following User Says Thank You to micromind For This Useful Post:
Old 07-10-2011, 10:45 PM   #8
This is the only other picture I have at the moment.
Old 07-10-2011, 10:49 PM   #9
Idiot Emeritus
That's almost certainly a 120/208 wye.
Old 07-10-2011, 10:49 PM   #10
And this one.
Old 07-10-2011, 10:51 PM   #11
I have to say I have been trying to read and understand all this electrical stuff and I have to give it you guys! This stuff takes a special person to understand all this and I am glad you guys are willing to help!
Old 07-10-2011, 10:57 PM   #12
kbsparky's Avatar
Your first picture shows an ITE 100 Amp 3 phase main.
The other pictures appear to be a single phase GE panel.
I doubt they are the same panel here. Do you have more than one panel present?
-KB
Old 07-10-2011, 10:59 PM   #13
kbsparky's Avatar
Not so fast. That load center looks like a single phase panel. THAT in and of itself points to a delta-connected service. Let's see if the OP can supply more photos, and information as to the number and location of any other panels present.
-KB
Old 07-10-2011, 10:59 PM   #14
Well the first pic is of the main breaker outside the building and the other is the panel inside the shop.
Old 07-10-2011, 11:02 PM   #15
kbsparky's Avatar
NOW we are getting somewhere. Are there any other panels in there? You could have a 3 phase main service outside, but only single phase available inside.
-KB
Three phase transformer question rongaudier Electrical 8 03-08-2011 07:19 AM
Converting 3 phase equipment to single phase /VFD? lightison Electrical 7 01-04-2011 03:14 PM
Wiring Single Phase through 3 Phase socket tonyr417 Electrical 10 10-26-2010 09:09 PM
Want to add a single phase Subpanel to three Phase Main meglomachinist Electrical 19 09-10-2009 03:46 PM
120/208/1 phase wiring questions JohnJon Electrical 11 08-31-2008 11:28 PM