Any Limit On Number Of Outlets Per Breaker? - Electrical - DIY Chatroom Home Improvement Forum
Old 03-18-2010, 09:02 PM   #1
Any limit on number of outlets per breaker?
Within the same area (in this case a 14x20 attached garage) would it be permissible to run 6-8 outlets and one light off a single 20 amp breaker? Assume the high number of outlets is for convenience such as being to plug in a shop vac where needed and does not reflect intent to use several at the same time.
Wondering too if a single GFI circuit in small garage is adequate or is there something mandating 2 such circuits?
Thanks for the help.
Mi Feller is offline   Reply With Quote
Old 03-18-2010, 09:40 PM   #2
Single circuit GFCI protected is all that is needed
No limit on the number of outlets
I'd run (2) 20a circuits myself
And I'd put the lights on a lighting circuit
Old 03-18-2010, 10:00 PM   #3
Thanks And...
Will run 2 circuits. One with the GFI outlets and another with lights and probably ceiling outlet for opener which doesn't need to be GFI if out of reach from floor level. Have larger detached garage which gets heavy use. This one just really for parking car. Thank you and good evening.
Old 03-18-2010, 10:08 PM   #4
Actually NEC 2008 did away with the exclusion for the door openers
Under NEC 2008 all outlets in the garage need to be GFCI protected
Old 03-19-2010, 06:45 AM   #5
Just call me Andrew
Rewards Points: 1,020
You can run a MWBC (multiwire branch circuit) for your outlets, then a separate lighting circuit. This would give you two separate outlet circuits and save money.
You run a 12/3 cable from the panel. White goes to the neutral bar, black and red each go to their own breaker. The breakers have to be next to each other (vertically) and be on different hot busses. They also have to be tied together with handle ties (or use a double-pole breaker) so they go on and off together.
Then run 12/2 or 14/2 for your lighting.
Andrew
secutanudu is offline   Reply With Quote
The Following User Says Thank You to secutanudu For This Useful Post:
Mi Feller (04-20-2010)
Old 03-19-2010, 07:56 AM   #6
Electrician
SD515's Avatar
Rewards Points: 504
Secutanudu...you should also mention that on a MWBC the neutral has to be "pig-tailled" at the points where devices are attached, ie. receptacles, lamp holders, so as not to break the continuity of the neutral if the device were to be removed. See 300.13 (B) Device Removal.
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
secutanudu (03-19-2010)
Old 03-19-2010, 08:07 AM   #7
Just call me Andrew
Thanks, Kyle. Didn't know that. Why does the fact that it's a MWBC make it more dangerous to disconnect a neutral than a normal circuit?
Here's that section of the code you mentioned, showing that you are correct:
Andrew
Old 03-19-2010, 08:50 AM   #8
Electrician
SD515's Avatar
Rewards Points: 504
I'm on dial-up, so it's not easy for me to jump around the internet and find a picture to be able to post here. I'll try, but someone else may beat me to it...which is fine with me.
If you were to lose the connection of the neutral, especially at the point of origin (the panel), the circuit instantly becomes a 240v circuit. Electricity is trying to find it's way back to the source, and will use any means possible. Example....Imagine no neutral connection at the panel...power leaves the black wire...goes through a TV (or whatever), returns to the receptacle, leaves the receptacle on the WHITE wire, goes to the next receptacle and enters on the WHITE, goes through a hair dryer (example) and leaves on the RED wire and goes back to the panel. With a properly installed circuit, the Black and Red wire would be on different busbars....hence 240V potential between black and red.
Kyle
Old 03-19-2010, 09:18 AM   #9
Just call me Andrew
Got it, thanks. I guess it'd drop down voltage due to the resistance in your loads...maybe to 180v or something?
Andrew
Old 03-19-2010, 09:42 AM   #10
Electrician
SD515's Avatar
Rewards Points: 504
Correct, depending on the resistance of the loads, which are now in series. And your example of dropping down to 180v most likely would fry that particular device.
Can't yet find the picture I'm looking for, but maybe these will help.
Kyle
Old 03-19-2010, 09:49 AM   #11
Just call me Andrew
Another thought...if one or both circuits in a a MWBC neeeds GFCI outlets (like the OP will need in the garage), would this require GFCI outlets at every location, since the outlets would have to be pigtailed? Put more simply, does 300.13 (B) prevent wiring downstream devices from the LOAD side of a GFCI outlet?
Maybe the best way to GFCI protect a MWBC is with GFCI breakers?
Andrew
Old 03-19-2010, 10:00 AM   #12
Master Electrician
Rewards Points: 3,920
GFCI receptacles work fine on MWBC's if they are installed correctly. You must fully understand both MWBC's as well as GFCI's. IMO untrained people should not even try to use MWBC's.
brric is offline   Reply With Quote
Old 03-19-2010, 10:29 AM   #13
Just call me Andrew
How are GFCI's properly installed on MWBC? As long as it is installed with pigtails, can you feed downstream outlets off the load side?
Andrew
Old 03-19-2010, 11:17 AM   #14
Master Electrician
See Stubies diagrams for GFI's on MWBC's.
delayed breaker trip flyrod Electrical 9 01-08-2017 08:57 AM
GFCI breaker trips randomly BimmerRacer Electrical 40 09-21-2009 02:11 PM
New GFCI Breaker trips with no load bmurphywa Electrical 6 04-06-2008 08:48 PM
Outdoor breaker panel questions lhoney2 Electrical 12 07-19-2007 05:44 PM
series of troubled outlets Swimmfst Electrical 9 06-14-2006 06:26 AM