Another Subpanel Grounding Question - Electrical - DIY Chatroom Home Improvement Forum
Old 06-11-2010, 09:06 AM   #1
I built a pole barn, ran (if I remember correctly) 1/0,1/0,2 aluminium Triplex to it with a 125A breaker. Bought the triplex for <$1/ft from our coop electric company. I made two significant errors though. The first is I used a subpanel without a main breaker. I bought a GE retrofit kit from the local electrical supply house yesterday. The second error was that I drove ground rods and grounded to them without running a discrete ground to the panel. This originally wasn't an issue however now that I want to run phone and satelite TV out there, I need to lay a ground wire (I think). All circuits (including lighting) are on GFIs. I have 2 extra runs of conduit that I can pull the ground through. The run is about 250' back to my main panel. What is the minimum size ground wire do I need for this run or do I even need it if everything is GFI protected? Also, what type of wire is recommended, THHN? Does it sound like I am missing anything else. Thanks!
behrend is offline   Reply With Quote
Old 06-11-2010, 09:17 AM   #2
I=E/R
a7ecorsair's Avatar
I think code requires all the wires to be in the same conduit. Also, your 125A breaker may not be correct for 1/0 aluminum.
If there are six or fewer disconnects at the pole barn you are really OK, but a building disconnect is nice to have.
a7ecorsair is offline   Reply With Quote
Old 06-11-2010, 10:49 AM   #3
Rewards Points: 254
You cannot run a separate ground wire to the panel. It must be in the same conduit or cable.
If you are on the 2005 code cycle or earlier you can use the 3 wire feeder. If you are on the 2008 cycle, you can start digging or pulling the wire out. The bonding wires from the rods go directly to the sub panel and land on the grounding bar.
See what code cycle you are on. We can address the rest once you get back with an answer.
PS......The 125 amp breaker is fine in the sub panel, as it is only a switch. You must use the correct size breaker in the main panel for the size and type of wire you are using.
J. V. is online now   Reply With Quote
Old 06-11-2010, 11:46 AM   #4
I=E/R
a7ecorsair's Avatar
JV, I think he is saying the 125 breaker is in the main service and the sub is a main lug.
Isn't the 1/0 AL only good for 100 amps at 60C?
Old 06-11-2010, 11:57 AM   #5
joed's Avatar
Rewards Points: 13,768
Yes but then
It doesn't matter what code cycle he is on. He now wants to run phone lines. Either code cycles requires four wire feed with phone lines.
Old 06-11-2010, 12:49 PM   #6
I am under the 2003 code. I'll check on the triplex, i can't remember if it is 1/0 or 2/0. Thanks.
The more I think about it, doesn't sound like it is worth the effort to be bothered by some telemarketer anyhow. If I ran satellite TV or ethernet out there, would I have to add the 4th wire for those as well?
Old 06-11-2010, 12:55 PM   #7
Any additional metal path between the buildings requires the 4th wire
You could run fiber optic
Old 06-11-2010, 01:21 PM   #8
Master Electrician
Rewards Points: 3,966
I believe the ampacity of directly buried URD is not governed by the 60 deg C. rating. It is not SE , SER or NM cable. Southwire lists one of theirs at 215 amps.
brric is offline   Reply With Quote
Old 06-11-2010, 01:30 PM   #9
So if I dug up the trench and added the 4th wire, what kind of wire and gauge would be appropriate? Thanks.
Old 06-11-2010, 01:41 PM   #10
Master Electrician
#8 Cu or #6 Al.
Old 06-13-2010, 10:08 AM   #11
Rewards Points: 254
You can't add another wire. You need to replace the cable or pull in a ground if you have conduit.
Old 06-13-2010, 10:22 AM   #12
Mad Scientist
You coud run fiber optic
Just to add to this, I would really recommend using fiber if you run ethernet over this distance. My previous employer had a 100' or so ethernet run between two buildings, and about once a month during summer storm season the switch on one end or the other would fry. We pulled in a length of fiber with a media converter on each end and that was the end of it.
You can get the media converters from Ebay pretty cheap, they're just a little box with a network jack on one end and fiber connectors on the other.
McSteve is offline   Reply With Quote
Adding second grounding bar to subpanel rdy2go Electrical 11 09-13-2009 07:59 PM
To Subpanel or Not to Subpanel, That is the Question finnimus Electrical 8 03-05-2009 02:32 PM
GFCI feeing subpanel question scott2332 Electrical 45 02-28-2009 03:15 PM
grounding to water pipe question eastvantrading Electrical 6 12-20-2006 09:49 AM
Question on Grounding ayudi General DIY Discussions 2 12-11-2006 04:14 AM