another "help me with a subpanel" topic
I've been conducting research on this forum but I still have a few qeustions I'd like to run by you guys and gals. I really want this install to future proof.
I am thinking about wiring my 10ft x 20ft detached shed for power. I am going to use a 100 amp subpanel which will be fed from either a 60 or 100 amp double throw breaker from my 200amp main panel. I will need to run about 30-40 ft of romex from the main panel to a junction box in the attic there I will splice it to either #6 or #3 THHN/THWN (depending on wether I use a 60 amp or 100 amp breaker), then run another 30ft of 2 hots and 1 neutral of THHN/THWN through a 1 1/4 inch PVC conduit which will be buried 18 inches underground. I will use #8 wire as a ground near the subpanel which I will attach to 2 grounding rods at least 6ft apart. I will need to isolate the neutrals from the ground as the installation will be in a detached building with it's own ground. I will installing eight 20 amp receptcales for power on a 20 amp breaker, the first receptacle will be a 20 amp GFCI receptacle and the rest will be wired in series. Five sets of 48 inch flourescent shop lights on another 20 amp GFCI circuit breaker. Lastly I might install a 30 or 50 amp 240v receptacle in case I want to buy a small welder in the future which will protected by either a 30 or 50 amp breaker depending on what plug I decide to go with. I will be doing the installation and applying for the permit, but I will be hiring an electrician to connect my wiring to the main breaker and inspect my work. I am currently reading the NEC guide and I am not an electrician so some of the things I want to do might be wrong.http://www.ar15.com/images/smilies/smiley_abused.gif What size romex do I use for the 30 ft run from the main breaker to the junction box in the attic, assuming I will use the 100amp breaker or do I just use the THHN/THWN in a conduit from the main breaker? Is #3 THHN/THWN big enough for 100 amps? Is there anything you see wrong with my plan? |
You will need to run 4 wires to the sub. The sub must have the ground and neutral seperated withing, and the neutral must not be bonded to the sub, but the ground buss must be. And for 100 amps you will need #2 wires for the hots and neutral and #6 for the ground from the main panel. What are you doing in that little shed that requires 100 amps? And I believe you will need 2 grounding rods at the shed as well. Get ready for a boat load of information coming your way from the professionals who migrate here.
Because #2 is rated for 100amps, #3 is not. If you don't need 100 amps, use #4 and install an 80amp breaker.
I am liking this idea:thumbsup: |
Print this out for future reference. Wire ampacity chart:thumbsup:
I would install #3 hots, #4 neutral and a #8 ground for such an installation. |
Look at it again...THHN is rated for 85 amps. Unless you are looking at service capacities...which this installation is NOT.
1 Attachment(s)
You need a vision exam.
TW, UF-B, and NM-B are rated at 85 Amps in that chart. RHW, THW, THWN, XHHW, SE, and USE are rated at 100 Amps. YOU LOOK AGAIN |
:surrender: I apologize, KB.....somehow I got fixated on the aluminum chart.:stupid:
Even on the aluminum side of the chart, you would be required to use a #1 conductor for a 100 Amp feeder.
Since you can't use the 90 degree column size if you terminate those wires on a regular circuit breaker or load center's lugs. They are only rated for 75 degrees max. |
To the OP....why so much power? I would be willing to bet that 30/240Vac would be plenty....you have 240Vac is you need it...but I doubt you will ever use more than 30A in your 'shed'. I have a lot of power tools in my garage along with a compressor....I have never tripped the old 30A breaker (except for the one time I drove a ground rod through the conduit...alcohol was NOT involved).....I now have it on a 50A....but I really doubt I will ever get close to it (especially if I keep the ground rods in check). |
While that may be true, it is much cheaper to provide two ground rods than to try and prove one rod has a 25 ohm resistance... which I doubt you could ever get with a 100 rods. :laughing: |
| All times are GMT -4. The time now is 04:31 AM. |