Amps Vs Wattage - Electrical - DIY Chatroom Home Improvement Forum
Old 05-29-2007, 11:40 AM   #1
Rewards Points: 256
Amps vs wattage
I've been looking to put in an electric tankless water heater which requires quite a bit of power. Looking at the charts it is reasonable to expect one that requires at least 80 amps, and I only have 100 through the meter right now.
So I had an electrician come out to give me a quote on boosting power and we got into a discussion about why I needed more. He started into a conversation of wattage vs amps, saying that even though they might require 80 amps, the wattage will say it draws much less power and I might not really need more than 100amps. I was confused and he wasn't very good at explaining the difference to me. I wasn't going to bring voltage into the equation.
So I went back to the charts and it confuses me further, I'll give you an example: The one I'm looking at says 208 volts, 14.4kw, 70 amps; OR 240 volts, 19.2kw, 80 amps.... and the 80 amps requires 2 50amp breakers.
I hope somebody has an easy way to explain this! Thanks!
moneymgmt is offline   Reply With Quote
Old 05-29-2007, 04:22 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,864
You need all three thing to figure load, and ALL are important. Wattage, voltage and amperage.
Wattage is what you draw, NOT amperage. The wattage is constant, the amperage goes up and down according to voltage.
Household voltage is 240v, more accurately 120/240v.
19.2Kw?!?!?????
Watts divided by volts equals amps. So....
19,200 divided by 240v = 80 amps.
There is NO WAY you will run this unit efficiently with only a 100 amp service to the house.
Upgrading to 150 amps is almost worthless. The difference to 200 amps cost wise is negligible, so I would not even consider 150 amps.
Old 05-29-2007, 06:22 PM   #3
joed's Avatar
Rewards Points: 11,964
You should also know that two 50 breakers means two 50 amp double pole breakers. That is four breaker spaces in your panel.
The reason the two voltages are listed is because you could use this heater in an industrial location where the voltage would be 208 volts. In you home the voltage is 120/240 volts.
Old 05-30-2007, 09:29 AM   #4
This is extreemly rare, but I do have to disagree with my friend Speedy on one point. Wattage is not the constant, resistance is. If you take an x watt 240 volt heater and install it on a 208 volt system it will draw less wattage, and the deta t rise will be less across the coil.
If a home has a 240 volt 100 amp service it would have a total of 24000 watts available. If only 120 volt loads were connected, you could have up to 200 amps of such loads. 24000/120.
Since most residential panels have a mixture of 120 and 240 volt loads the only practicle way to add them together is to convert them all to wattage, add them, then divide by the system voltage 240.
As to the OP original question.
KW / Volts = Amps ..... Volts / Amps = Ohms
If you do the math on your appliance you will get 3 ohms at either voltage.
I agree with Speedy that upgrading to 150 amps is a waste of time and money. I also think you will be disappointed with your higher electric bill. I have no direct experience, but have heard of alot of people who were disappointed at the savings after installing tankless water heaters. Either the number of years to pay off were longer than the customer expected to live, or the electric usage actually went up.
Master Electrician
jwhite is offline   Reply With Quote
Old 05-30-2007, 09:33 AM   #5
Rewards Points: 256
19.2Kw?!?!?????
Ok, i get the 240 vs 208 and that is what I figured the difference was. So if voltage is constant, wouldn't watts and amps be in direct relation? A better way to ask it, how can wattage tell me something that amps do not?
And Petey, can you elaborate on "19.2Kw?!?!?!?!" I'm assuming you thing that's a sick amount of power to be drawing? I do know that if I increased I'd likely go to 200 vs 150amps. The other idea that I kicked around was adding another meter and shutoff panel just for the water heater..... that would be even cheaper than upgrading the entire service.
Thanks all!
Old 05-30-2007, 10:12 AM   #6
Not to speak for Speedy, but 80 amps is a sick ammount of power for a 100 amp service. The service should only be loaded to 80 percent to start. 80 amps on a 100 amp service would max it out with just the water heater.
The second service may not be an option. Check with your utility company. They may not allow this for a single family home. In addition find out the monthly cost for service and minimum kwh. Then figure out how many years it would take for the extra utility bill to equal the cost of a 200 amp service install.
Master Electrician
Old 05-30-2007, 01:39 PM   #7
Rewards Points: 256
Good stuff, thank you. The whole discussion started because the electrician was in some way trying to tell me that even though it needs 80 amps it probably didn't use that much power..... I have no idea, thus the post.
As far as the separate service, billing wouldn't be an issue, there is no minimum on electricity (just gas). He did tell me to call the power company first and ask if this was an option on my home.
Old 05-30-2007, 03:50 PM   #8
JW is completely correct. I should have been clearer in my explanation. I must admit, theory is not my strong point.
Thanks Jeff for the clarification.
Old 05-30-2007, 08:13 PM   #9
weekend warrior
Rewards Points: 150
it can't, they're directly proportional.
wattage = voltage x amperage
(ohms law)
johnny331 is offline   Reply With Quote
Mini refrigerator wattage? kcrossley2 Electrical 8 04-16-2010 04:06 AM
480 voltage to 200 amps girl who needs info Electrical 1 08-01-2007 05:48 AM
splitting 200 amps, help with parts please tuolumne Electrical 2 03-30-2007 01:09 PM
Upgrading Service to 200 amps sandyman720 Electrical 6 03-30-2007 06:37 AM
Amps to Watts Darylh Electrical 14 06-26-2006 12:57 PM