I have a whole house power monitoring system that I use to monitor my power usage. It outputs so many pulses for every watt used across the two legs.
I am working on a formula to show me the current AMPs and watts being used.
When I put my clamp on meter on one of the 120 VAC legs at the meter, it'll read say 10 amps and the other leg might read 15 amps, so I am using 25 amps of power, correct?
So 200 amp service means each leg can handle up to 100 amps and when you add the two together that is where the 200 amp rating comes into play?
-Andrew
DIY hobbiest
AndrewF is offline   Reply With Quote
Old 02-16-2009, 07:50 PM   #2
Idiot Emeritus
Rewards Points: 1,492
If you have a 200 amp service, each leg is capable of 200 amps.
Rob
micromind is offline   Reply With Quote
Old 02-16-2009, 08:10 PM   #3
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Yes you add the 2 numbers to get your total use.
Jamie
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 02-16-2009, 08:18 PM   #4
joed's Avatar
Rewards Points: 13,368
It is all a matter of reference.
You are using 10 amps at 240 volts and 5 amps at 120 volts.
OR
You are using 25 amps at 120 volts
In both cases you are using 3000watts.
Edit: to correct the numbers. I misread as 15 amp on one leg and 25 on the other instead of 10 and 15.
Old 02-16-2009, 08:46 PM   #5
120V x (10+15)A = 3000W?
200A x 240V = 48kW.
24kW/120V = 200A.
Can you post a make and model for your power monitor?
Why not just read your PoCo meter?