AL Splice - Electrical - DIY Chatroom Home Improvement Forum
Old 11-27-2012, 11:45 PM   #1
Rewards Points: 528
AL splice
I dont think i can go this route but will ask before i end up buying another extremely long piece. If i have # 4 AL bare ground going from neutral bar to copper water pipe and need to extend the Al wire can i use this Al splicer wire lug ? or any other approved AL connector .AL splice-imag0174.jpg
hidden1 is offline   Reply With Quote
Old 11-27-2012, 11:50 PM   #2
" Euro " electrician
frenchelectrican's Avatar
Are you upgrading this service or what ?
Normally I use compession connection that is the only thing I ever use on larger alum espcally with EGC ( electode grounding conductor ) I know there are other approved items but it depending on your state/provice is.
Merci,
Marc
Old 11-27-2012, 11:53 PM   #3
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
The GEC must be continuous from the main disco to the electrode (whether its the rods, water, ufer, building steel...). I know you can purchase irreversable crimp connectors that would allow you to extend the wire, but the cost of the crimper is more than a new run of wire.
Old 11-27-2012, 11:58 PM   #4
k_buz's Avatar
From NEC 2008:
(C) Continuous. Grounding electrode conductor(s) shall
be installed in one continuous length without a splice or
joint except as permitted in (1) and (2):
(1) Splicing shall be permitted only by irreversible
compression-type connectors listed as grounding and
bonding equipment or by the exothermic welding process.
(2) Sections of busbars shall be permitted to be connected
together to form a grounding electrode conductor.
From NEC 2011
(C) Continuous. Except as provided in 250.30(A)(5) and
(A)(6), 250.30(B)(1), and 250.68(C), grounding electrode
conductor(s) shall be installed in one continuous length
without a splice or joint. If necessary, splices or connections
shall be made as permitted in (1) through (4):
(1) Splicing of the wire-type grounding electrode conductor
shall be permitted only by irreversible compressiontype
connectors listed as grounding and bonding equipment
(3) Bolted, riveted, or welded connections of structural
metal frames of buildings or structures.
(4) Threaded, welded, brazed, soldered or bolted-flange
connections of metal water piping.
The Following User Says Thank You to k_buz For This Useful Post:
frenchelectrican (11-28-2012)
Old 11-28-2012, 06:16 PM   #5
Rewards Points: 528
10 Cable Junction Box Splice swstx Electrical 8 07-06-2010 09:16 PM
splice in electrical box dmilne Electrical 2 02-25-2010 10:59 AM
50 Amp Circuit - Splice 6 Gauge Cable to 12-3? jodic Electrical 4 01-23-2010 12:10 PM
to splice or not to splice treedoc Electrical 4 01-19-2008 10:56 PM
Splice box/s between subpanel and main panel? SeanR Electrical 5 05-06-2007 02:21 PM