Old 11-15-2012, 10:11 AM   #16
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
You have a dedicated 120 V / 20 amp circuit and a 120/240 volt motor. Convert the circuit and the motor to 240. The motor will be more efficient and draw half the amps. Replace the breaker with a 2 pole and replace the receptacle and plug (less than $40 material).
Coastal South Carolina
Old 11-15-2012, 10:37 AM   #17
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Originally Posted by micromind View Post
What type of breaker?
Inverse time CB.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 11-15-2012, 08:38 PM   #18
Idiot Emeritus
Rewards Points: 1,492
Originally Posted by electures View Post
Inverse time CB.
What brand and age?
For example, the older Square D breakers had a pretty high magnetic trip, the newer ones are very likely the lowest in the industry.
If it's an arc-fault, it'll absolutely trip with a motor that size.
Some (if not all) manufacturers make a 'high magnetic' version of their standard breakers; this would likely solve the OPs problem.
I agree with the others, if it's a dedicated circuit, and there's room in the panel, I'd highly recommend changing it to 240.