I've never done this, but is there a code that says you cannot install a contactor inside a panel, even if there is adequate space? See NEC 312.8
uconduit is offline   Reply With Quote
Old 10-08-2011, 05:27 PM   #2
Electrical Contractor
kbsparky's Avatar
312.8 requires adequate space. If you have sufficient space, then you're good to go.
-KB
Old 10-08-2011, 05:28 PM   #3
Electrician
SD515's Avatar
Rewards Points: 504
Never seen it done that way, but I suppose you could, if the contactor didn’t fill the area it’s in over 40%. All the wires connecting to it (and I would think the contactor itself) would have to be rated for the highest voltage present in the panel. Many wires would be, but some lower voltage wires may not be. Most of the time contactors are mounted in a separate box next to, or remotely away from the panel box.
Kyle
Old 10-08-2011, 06:47 PM   #4
Code05's Avatar
Rewards Points: 1,104
These are real handy items.
http://www.functionaldevices.com/building-automation/
Code05 is offline   Reply With Quote
Old 10-08-2011, 11:19 PM   #5
Looks like I will do that. I know it's not encouraged, but there is absolutely nowhere else to put it! Thanks.
Lighting proximity to outdoor hot tub - Code Question jeffinpickering Electrical 0 09-12-2011 02:43 PM
Bryant Plus 90 Code 31 ~kirkland~ HVAC 1 03-08-2011 07:14 PM
2008 NEC Code & AFCI Requirement theatretch85 Electrical 5 03-12-2009 10:58 PM
Another Bryant 383KVA with code 31 problems rpgIVguru HVAC 1 02-05-2007 02:47 PM
International building code and permits rforsha Building & Construction 4 08-28-2006 07:35 PM