According to Mike Holt:
The major problem is that some installers do not yet understand how the AFCI circuit protection device operates. If there is a neutral-to-ground connection on the load side of the circuit breaker, the breaker will not trip until a load has been applied, whereas a GFCI, even without load, will not operate until the neutral-to-ground connection has been removed.
What occurs is that the electrician leaves the property after installing and turning the devices on, then the homeowner calls two hours later complaining that there is no power. Trouble-shooting determines that as soon as a load is applied, the AFCI trips because of a faulty neutral-to-ground connection on the load side of the device.
What is he talking about exactly when he mentions a "neutral-to-ground connection on the load side of the device"?
Randell Tarin is offline   Reply With Quote
Old 06-04-2008, 05:55 AM   #2
Licensed Pro
This usually occurs when there is contact between the bare ground wire and the neutral (silver) screws of receptacle due to sloppy installation of the receptacle in the box. A GFCI will trip as soon as power is restored. An AFCI will trip when a load (lamp, appliance) is applied to the circuit.
Old 06-04-2008, 05:58 AM   #3
what is AFCI and GFCI.
I think we use diferrent terms.
RCD,
RCBO etc.
Could you please let me know what it stand for.
mpj111 is offline   Reply With Quote
Old 06-04-2008, 06:10 AM   #4
electrical contractor
Rewards Points: 150
AFCI- Arc Fault Circuit Interrupter
GFCI- Ground Fault Circuit Interrupter
Jimmy
Life is tough, Life is tougher when you are stupid.
wire_twister is offline   Reply With Quote
Old 06-06-2008, 02:38 AM   #5
" Euro " electrician
frenchelectrican's Avatar
RCD = Resdentail Current leak Detector. It is simuiar to the North American verison of GFCI device but however the tripping level is diffrent then GFCI are. Most RCD are set at about 30~50 MA depending on manufacter and spec level per local reqirement.
Merci,Marc
Loose electrical outlets travishume Electrical 30 08-01-2008 07:21 PM
New AFCI requirements fw2007 Electrical 16 04-07-2008 08:52 AM
Tripping Wrong Breaker woodworksnmore@comcast.ne Electrical 15 03-28-2008 01:47 PM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 08:59 PM
Ring Circuit Tripping Loftus Electrical 4 05-28-2007 03:58 PM