Old 12-09-2012, 09:16 PM   #1
adding a switch to an outlet with two circuits
I'm trying to do some under cabinet lighting. I found the 15 amp circuit that runs the kitchen and foyer lights. I added up all the wattage and it can handle more lights. I was thinking I could add another switch to the existing outlet to control the under cabinet lighting. I've been following this tutorial on The Family Handyman
But, my setup isn't exactly the same because I want to tap into an outlet that controls a kitchen light. This outlet also controls the garbage disposal (on a different circuit that also has the dishwasher). See my diagram.
http://t.co/qxgxDQ9R
Circuit A - holds the dishwasher and disposal (20 amp)
Circuit B - holds the kitchen light and is the circuit I want to tap into
Assume everything is grounded. I just didn't draw it.
So, my question is how would I add a new line into the box on circuit B? Just add a new line and connect the blacks before it goes into the switch?
jeffpeter is offline   Reply With Quote
Old 12-09-2012, 09:46 PM   #2
Missouri Bound's Avatar
I take it this is a MWBC?
Do you want it your way or the right way?
Old 12-09-2012, 10:18 PM   #3
Multiwire branch circuit? Not sure. The switches do all share the same neutral. However, everything is grounded inside the outlet box. The switches are in the same box, but are two different circuits.
Old 12-09-2012, 10:22 PM   #4
The switches share the same neutral? Hmm...what neutral? If you have two circuits and they share the same neutral then it's a MWBC...if it's NOT a MWBC then you have a problem. How many breakers turn off everything...just one?
Old 12-09-2012, 10:35 PM   #5
Two breakers are required to turn off everything. One controls the disposal & dishwasher (20 amp). One controls the lights (15 amp). The switch on the right in my diagram controls the disposal. The switch on the left controls the light.
I don't know what neutral they share. Are you asking if the shared neutral goes back to the 15 amp or the 20 amp? I have no idea. Both? I thought it was weird that they'd share the same neutral when I opened the box. All five white wires in the box are connected with one wingnut.
Old 12-09-2012, 10:37 PM   #6
I don't want to complicate your issue, but if both breakers share a neutral it's a MWBC. And if those breakers aren't tied to gether with a common trip bond it's an illegal installation. You may want to get that taken care of before your remodeling project.
Old 12-09-2012, 10:42 PM   #7
How would I tell if the breakers were tied together with a common trip bond?
Old 12-09-2012, 10:43 PM   #8
Licensed Electrician
k_buz's Avatar
That still isn't mandatory in some places. That code was put into effect for the 2008 code cycle. There is no requirement to replace the breaker if it wasn't required when the circuit/s were installed.
Location...Location...Location
Old 12-09-2012, 10:45 PM   #9
House was built in 2000 in NC. I hear we have very relaxed building codes...
Old 12-10-2012, 07:28 AM   #10
Not as dire as Missouri makes it out to be. Just be sure to turn each of the breakers off when working on either of the circuits because current on the neutral conductor can bite also. Post a note on/in panel that circuits X & Y are part of a MWBC as a reminder to turn off both breakers.
As long as each of your hots are attached to a breaker on separate buses of the panel...meaning the breakers are put in next to each other as the photo below..... the 2 hots can share the same neutral. You may have to make sure that the breakers are tied together with a handle-tie....like the photo below.
hammerlane is online now   Reply With Quote
Old 12-10-2012, 07:43 AM   #11
Here are 3 ways of doing it based upon whether you run power to the switch location first or to the light location first. Diagram #1 takes power to the switch location first. Diagrams #2 and #3 take power to the light location first. Also diagrams #1 and #3 have a neutral conductor at the switch location and diagram # 2 does not.
No ground wires shown for ease of drawing.
adding a switch to an outlet with two circuits-a9ubjbicaaa6h7u-1.jpg   adding a switch to an outlet with two circuits-a9ubjbicaaa6h7u-2.jpg   adding a switch to an outlet with two circuits-a9ubjbicaaa6h7u-3.jpg
Old 12-10-2012, 10:16 AM   #12
OK OK...I'll quit yelling "the sky is falling"
But it's imperative that the circuits be on opposite "phases" of the panel or the neutral can be overloaded. That's one of the purposes of the two pole breakers. The other is to assure that both circuits are energized or off at the same time.
Old 12-10-2012, 10:17 AM   #13
Old 12-10-2012, 08:41 PM   #14
This is what my breakers look like. They're not right next to each other... Am I still okay to share a neutral?
Old 12-10-2012, 08:49 PM   #15
Licensed electrician
Those breakers are on the same leg of the panel. If they are sharing a neutral there is a potential to overload it.
I would question whether this is a MWBC based on the 15 and 20 amp breaker sizes.
Tags
circuit, lighting
Adding Light Switch - Outlet - Light > Correct wiring ? westbank Electrical 4 09-15-2012 11:42 AM
Kitchen Electrical: one switch for multiple circuits esotericaqua Electrical 8 06-22-2012 06:09 PM
Adding new GFCI outlet to existing light switch idzrvit Electrical 15 11-20-2011 10:16 PM
Just for fun Andy in ATL Electrical 56 10-20-2009 10:33 AM
HowTo: Adding two exterior lights + switch, piggyback new switch off existing switch? ghost Electrical 14 04-19-2009 06:04 PM