Adding a subpanel to a sub-panel and other questions
Just found this site and have a few questions.
I recently had a new metal building built that will be both garage, RV storage, shop and office. I had a licensed electrical contractor do the initial wiring to bring service from my house to the building. Here is what he did:
Questions:
You did not say how the feeder wires were installed out to the new building. Overhead or underground? It is a shame that the contractor put such a small breaker box in. :no: Before I added another sub panel, and worried about using twin breakers (some people call them slims), I would turn off the breaker back at the house and remove the 8 circuit panel and replace it with a 20 circuit Main Lug Only (MLO) panel. Reuse the 70 Amp DP breaker as a main and have plenty of room for full sized breakers. Twins or slims are more money than regular breakers, besides getting twins for 220V (then called Quads) is tough and very costly.
As for the heaters and all other loads, you only load the breaker up to 80% of it's rating. So you will need a 30 AMP DP breaker [25 amp breakers are not to common] As a sub panel from the house / main service, the neutral should not be bonded to the panel or ground rod, add a ground bar to your panel. |
If there are no other metallic paths between the two buildings (phone, cable, etc.) then the three wire feeder to the subpanel is acceptable and the neutral and ground bars should be bonded. Since this is a detached building, you MUST have a disconnect at the sub (you cannot use a MLO panel here). The installed grounding rod is correct, and the metal of the building should be bonded to this also.
There is no problem with adding another subpanel, but it might be better to swap out the existing with a larger one if you really need more circuits. Personally, I think 8 should be enough. What is the wattage of the heaters? |
My tip to replace the existing panel with a 20 circuit MLO panel.... continues on to say... to use the 70 amp DP breaker as the main breaker.
The reason is, they do not sell a load center with a main breaker smaller than 100 Amps. If the HO was to install an additional sub panel, he would have to buy a Double Pole breaker to feed the sub panel with plus the sub panel. It is cheaper and neater to just change out the panel with a 20 circuit MLO and use the 70 amp DP breaker as the main. |
Sub panels require a 4 wires and a main breaker. 2 hots 1 neutral and one ECG. The ground "ECG" should not be bonded to the neutral terminal strip. A lug panel cannot be used as the primary sub panel in this scenario. The additional sub panel can be a lug panel if it is in sight of the main subpanel and contains no more than (I don't know how many) breakers.
There is an exception, by making the sub panel a main service panel. But I am not certain the on the rule? You can go to 100 amp lug panel and mount a 70 amp main breaker in it if you want. Just install the breaker as any other and connect the feeder wires to it. Mark it "Main Breaker" Do not connect neutral and ground to together. You may need a ground terminal strip if one did not come with the panel. Your panel may have two terminal strips running horizontally along the sides of the interior. These are usually bonded from the factory. Just remove the the bar that connects the two and use one for grounds and one for neutrals. |
Allows a detached building to be fed with three wires and have the panel neutral and grounding bus to be bonded. There must be no continuous metallic paths between the buildings. Sorry michael, I missed the part about reusing the 70A breaker. It is also permissible to feed a subpanel that contains a 100A disconnect from a 70A breaker at the main panel and still comply. |
Housekeep, you are correct about being able to use a 100 Amp main breaker being fed from the 70 AMP DP breaker back at the main house. The only problem I have with that practice is, if the main should trip, it would trip first back at the house and require going over to the house to reset the breaker.
True, unless it is a dead short, then it's a crap shoot as to which would trip first.
Can I chime in? Although this installation is code compliant according to 250.32(B)(2), there are dangers involved.... The OP and everyone who ever lives in this house MUST be sure there are never any continious metal paths between the two buildings. There, imho, are NO circumstances where I would install this sub this way. Anyone agree? That pesky "parallel neutral path" scares me....alot...
I agree Andy, and I would not install a sub in a detached building this way. However, the OP asked if it was done correctly, and according to the NEC it was.
Thanks for all the info. Sorry I didn't chime in earlier, but I've been out of town.
This is a new metal building built on another lot next to the one I currently own (that has the house on it). Since I built the house and now the shop, I can guarantee there is no path between the two buildings. The service to the subpanel was installed underground with #4 aluminum wire. The reason I want more circuits is because I would like to have lots of outlets so I don't have to use cords or move equipment around. The load at any one time should be very small. Other than the heaters, and my table saw, the load should be fairly small. I guess I can put lots of outlets on one circuit, but thought this was a better way to go. I may rethink this after reading everyones comments. Thanks much!:) |
Its good this thread is this old. 2007! If the OP had posted this exact question today and his locality is now on the 2008 code cycle or newer the install would not be compliant. The 2008 code removed the exception and a four wire feeder would have been required.
Juneau. On a three wire feeder to a detached structure, the neutral, grounds and grounding electrode conductor (wire to ground rod) are all connected together. Exactly like the main panel. You cannot have any other metal paths other than the three wires. Note: This was only allowed until the 2008 code cycle. Or you locale had not adopted the 2008 as of the install date. Your only recourse is to remove the other metallic paths or update the feeder to four wires. I know of no exceptions as this a safety issue. Maybe someone will have some ideas, that will be more helpful to you.. |
Thanks JV,
So, if I add the 4th wire: What kind of wire? Does it matter if bare or insulated? Same gauge (#4)? Can I leave the other buried run in place? Does the bonding requirement in the garage panel change? Does the tiny (18-22 gauge, 4-pairs?) ADT alarm wire count as a continuous metallic path? I am considering removing only the 3-way light switch wiring. I need the security alarm more than the convenience switch these days. |
WHO KEEPS digging UP these OLD threads arrrrrggggg! ahoy mate |
| All times are GMT -4. The time now is 12:55 AM. |