Adding A Subpanel (lots Of Questions) - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 02-15-2009, 06:51 PM   #16
Rewards Points: 77
So Bob, are you saying that this sub panel here isn't going to work? Do I need to go buy a new one that has a disconnect on it, install a 100a disconnect in it, and then put a 60a feeder in the main panel?
Also, the city I live in uses 2008 NEC codes, does that mean I should still use 6/3 cable?
epeterson777 is offline   Reply With Quote
Old 02-15-2009, 07:15 PM   #17
Electrician
A subpanel attatched to the same structrure DOES NOT REQUIRE A DISCONNECT.
chris75 is offline   Reply With Quote
Old 02-15-2009, 07:19 PM   #18
Rewards Points: 266
Originally Posted by Bob Mariani View Post
The sub panel will still need a disconnecting means. NEC 230.79(D) All Others (more than two circuits in a dwelling) The service disconnecting means shall have a rating not less than 60 amps.
Article 230 covers services not feeders.
junkcollector is offline   Reply With Quote
Old 02-15-2009, 07:29 PM   #19
Originally Posted by chris75 View Post
A subpanel attached to the same structure DOES NOT REQUIRE A DISCONNECT.
Is that as long as everything can be shut off with 6 flips?
IE 6 breakers or less?
Or is that for detached buildings?
Yeah we went thru 230 on another thread, or maybe it was another board
Old 02-15-2009, 07:45 PM   #20
Rewards Points: 508
Send a message via AIM to theatretch85
I don't believe it matters whether or not there are 6 breakers or more, so long as it is in the same structure as the main panel/service disconnect.
And I believe it was article 225 that was being talked about most recently in other threads which covers "Outside Branch Circuits and Feeders".
To the OP, you should be ok with that panel as your sub.
theatretch85 is offline   Reply With Quote
Old 02-15-2009, 08:55 PM   #21
Electrician
ctsmiths's Avatar
Rewards Points: 150
The sub panel will still need a disconnecting means. NEC 230.79(D) All Others (more than two circuits in a dwelling) The service disconnecting means shall have a rating not less than 60 amps. But as a practical matter it would not make any sense to run something smaller. Especially since most agree to move several circuits to the new panel. And future needs are to be considered by code and practice also.
For inspection all connections should be done. Panel covers better be on. You remove them when he is there and asks you to. Safety. Never leave a panel cover off if its hot. Be sure to separate the grounds and commons (ungrounded conductor) on the sub panel. And if you move the wires to a range or dryer that is electric these too need new plugs (4 wire not 3 wire)
This install is covered in 408 in the nec not 230
ctsmiths is offline   Reply With Quote
Adding a subpanel to a sub-panel and other questions CardinalPilot Electrical 14 03-30-2011 02:23 PM
Painting a room for new baby. Lots of questions. SuperAkuma Painting 15 01-01-2009 10:18 AM
main subpanel questions rsriverrat Electrical 34 11-04-2008 11:57 PM
Considering Cork for Basement ... LOTS of questions! :) njchan Flooring 5 01-26-2008 08:05 PM
Subpanel questions wease Electrical 1 12-07-2006 01:39 PM