#1 |
Adding Service to Attached Garage
I want to add a 100A service to my attached garage and had a couple of questions. I currently have a 100A service in my basement which is maxed out (definitely problematic). I had a thought I'd like to run by the group. I was contemplating adding a 200A box in the garage next to the meter where the service for the existing box in basement enters the house. From there I would like to move the existing lines to that 100A service to make it a pony from the new 200A and tie the 200A to the external cutoff box (right below the meter). I could then tie my existing garage outlets, lights, hot tub, etc to the new 200A box and free up some capacity in the basement.
Is this feasible? How easy would it be? Is there a easier way? Am I oversimplifying this? TIA Steve |
#2 | |
Adding Service to Attached GarageQuote:
Upgrade the existing 100 amp service to 200 amp. The meter and disconnect will feed the 200 amp new panel. Feed the existing 100 amp panel from the new 200 amp service. This will allow you to put the 100 amp sub anywhere you want it. If you use the 100 amp panel as the service, you only have 100 amp capacity. Of course you will have many more breaker spaces than you have now, but still only 100 amp capacity. You will most likely need a new meter can, disconnect and larger wire. Is this why you want to keep the 100 amp as your service panel? You will need to involve the utility and the codes dept in your area. Get a permit first and talk to the inspector for his requirements. |
#3 |
Tool Geek
Ditto on J. V.'s advice. When I upgraded to 200 Amp, I had to go through both the Los Angeles City DWP for meter placement rules and the Building & Safety department for the permit that had to be submitted with a specific plan.
Call the Building dept and get their permit requirements first. Good Luck and report back on your progress. There are a lot of knowledgeable sources like J. V. that can help with advice.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. & Stay Safe .....Bob Lavery |
#4 | |
Would it be easier/cheaper to just replace the outside box with a doubletap and put a new 100A box in the garage? |
#5 |
so, you have a panel in the house and in the garage?...
#6 |
Adding Service to Attached Garage |
#7 |
#8 | |
The meter main type of panel has a few breaker slots outside. That gives you the ability to run circuits outside if needed. It will also make your 200 amp lug panel a sub panel, requiring no main breaker. The meter main will have the disconnect/breaker and lugs already installed. Good idea. Make sure you get a permit. Believe it or not, some inspectors will help you out. Not physically for sure. Last edited by J. V.; 03-20-2009 at 01:31 PM. |
#9 | |
#10 |
Good Luck Steve. Keep us posted and ask questions.......John
#11 |
All the above is good advice but to answer your question yes you can up grade to a 200 amp service in the garage and use the 100 amp panel in the house as a sub panel. You may have to make some grounding changes. Because it is all one structure you will probably have to disconnect the ground wire from the sub to the ground rode and run a wire from the ground rod to your new panel. The inspector should be able to supply the information you will need.
#12 | |
Ground wire? If he upgrades to 200 amp, he's going to have to upgrade everything, and maybe even drive another rod.
#13 |
Yes I did but wonder if you did. You said "You can use the existing 100 amp sub panel for the garage" The op wants to leave the 100 amp panel in the house and put the 200 in the garage converting the 100 amp panel to a sub feeding the house not the garage. Once converted to a sub panel the ground to the rod should be removed from the sub-panel and a new ground would have to be installed to the new main panel. And the common and ground would have to be seperated.
#14 | |
If he wants to re-use the 100 amp panel that is. |
| Display Modes | |
| Remodel - Moving from 200 amp service to 320 amps | stevedar | Electrical | 20 | 11-29-2009 09:14 PM |
| adding circuits to my 200 amp service | ssscamaro | Electrical | 4 | 01-19-2009 05:48 PM |
| Service line from house to garage.... question | Todd-sta | Electrical | 24 | 11-10-2008 01:23 PM |
| upgrading service for added garage | jakeb | Electrical | 12 | 03-29-2008 01:18 PM |
| Adding on to house to build a garage. | Ohioguy | Building & Construction | 5 | 02-09-2008 05:44 AM |