Adding The Neutral From Main To Subpanel - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 04-04-2010, 05:19 PM   #16
Just call me Andrew
Rewards Points: 1,020
Originally Posted by H2O Engr View Post
^^ secutanudu - if adding a UL-listed neutral lug like the one pictured above, would it have to be listed by the manufacturer for use with that specific electrical panel or could it be used in any panel assuming it's installed properly (solidly mounted, securely fastened, adequate contact surface, etc.)?
Not sure...I'll let an expert chime in.
Andrew
secutanudu is offline   Reply With Quote
Old 04-04-2010, 06:44 PM   #17
" Euro " electrician
frenchelectrican's Avatar
Unforetally with the OP's panel that have HOM series it will have to use the proper UL-listed netural connecter like that to spefic brand due each manufacter have diffrent netural bussbar set up so they are not really interchangeable at all.
Merci,Marc
Old 04-04-2010, 07:37 PM   #18
Rewards Points: 506
What is the logic for prohibiting multiple conductors in a terminal? Safety? Do two or more conductors prevent proper tightening? Or, what makes a terminal which is listed for multiple conductors different from one that is not?
jlmran is offline   Reply With Quote
Old 04-05-2010, 12:49 AM   #19
Licensed electrician
Rewards Points: 1,780
One neutral per hole is what is allowed by the NEC and also by the manufacturers instructions.
Whether multiple grounding conductors can be used is determined if the panel was listed that way by UL or another testing agency.
Old 04-05-2010, 07:04 AM   #20
Keep in mind a neutral is considered a load carrying conductor
So you would need to shut off both breakers for the neutrals
Every neutral would need to be marked in order to loosen a screw with (2) neutrals under it
Now add in a MWBC that might be one of these neutrals
Loosen that neutral & you have a 240v circuit
Might be other reasons but thats what comes to mind
Old 04-05-2010, 07:12 AM   #21
Master Electrician
Rewards Points: 3,920
The main reason is the heat produced by the current.
brric is online now   Reply With Quote
Old 04-05-2010, 10:33 AM   #22
Master Electrician
exactly...heat is the main concern.
I'd like to add to that, that over time the wires will loosen from expanding and contracting with the heat as well. The connection will loosen much faster with two wires under the lug than with one.
andrew79 is offline   Reply With Quote
Main disconnect neutral wiring Daniel Holzman Electrical 5 10-04-2009 01:36 PM
Adding a subpanel BimmerRacer Electrical 20 04-01-2009 08:30 PM
add subpanel or replace main panel... red86yota Electrical 3 12-04-2008 09:43 AM
Help if it's not too late!! Cyndi Electrical 255 10-10-2008 09:18 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 11:33 AM