Adding The Neutral From Main To Subpanel - Electrical - DIY Chatroom Home Improvement Forum
Old 04-03-2010, 11:29 PM   #1
adding the neutral from Main to subpanel
I know that I need to keep the neutral and ground wires separated on the subpanel but can they be combined on the main panel since they will be anyway?
for example, can I put the white neutral wire into the same location that the earth ground is going into on the main panel (circled in red)? Reason I ask is that the white neutral wire is too thick to fit into the bus bars on my main panel.
russellm is offline   Reply With Quote
Old 04-04-2010, 07:09 AM   #2
Earth, gnd, and neutral are connted together in the main panel. Earth and ground are connected together in the sub-panel. Neutral is floating, its' buss bar is isolated from the metal box, and from ground.
Side comment, sloppy looking panel. Would not impress an inspector.
Old 04-04-2010, 07:15 AM   #3
Master Electrician
Rewards Points: 3,966
Doubling wires under the same terminal is a no no unless the terminal is listed for multiple conductors.
brric is online now   Reply With Quote
Old 04-04-2010, 07:37 AM   #4
Electrician
Rewards Points: 802
Unless you have a seperate disconnect before this panel i would go no where near that lug with your hands. The two blacks would be hot and unfused and you could cause some serious damage to yourself, your house, or the POCO equipment.
darren is offline   Reply With Quote
Old 04-04-2010, 07:55 AM   #5
Electrician
SD515's Avatar
Rewards Points: 504
The NEC (US) prohibits 'doubling' of any neutral conductor at its termination. One screw, one wire.
I would shop for a listed ground bar for your panel, install it (power OFF of course), and terminate the main panel ground and the sub-panel ground on it. That will free up the terminal you have circled in red to use for the sub-panel neutral.
Keep in mind, that this is not necessarily a procedure for the novice do-it-yourselfer. I would consider having an experienced electrician do it.
Kyle
Old 04-04-2010, 07:56 AM   #6
Electrician
SD515's Avatar
Rewards Points: 504
Good point Darren.
Kyle
Old 04-04-2010, 08:03 AM   #7
Just call me Andrew
Rewards Points: 1,020
You can buy a lug for your neutral bus bar so you can fit the neutral wire in, like this:
Andrew
secutanudu is offline   Reply With Quote
Old 04-04-2010, 08:59 AM   #8
Master Electrician
IMO the grounding electrode wire, the bare wire in the photo, needs to remain on the neutral buss not be relocated to the equipment grounding bar. I would suggest doubling up enough equipment grounds in the existing panel (the bare wires) to give yourself enough room to install the listed lugs as shown above for the sub panel neutral and equipment grounds. It is acceptable to double up equipment grounds because they are not current carrying conductors as are the white neutrals. The new lugs should be 'listed' for the brand panel you have which appears to be a Square D Homeline.
Old 04-04-2010, 09:11 AM   #9
Weekend Warrior
^^ secutanudu - if adding a UL-listed neutral lug like the one pictured above, would it have to be listed by the manufacturer for use with that specific electrical panel or could it be used in any panel assuming it's installed properly (solidly mounted, securely fastened, adequate contact surface, etc.)?
brric - would the lug need to be listed for the specific model (Homeline) and not just any Square D-manufactured panel?
H2O Engr is offline   Reply With Quote
Old 04-04-2010, 09:14 AM   #10
Master Electrician
See above.
Old 04-04-2010, 09:16 AM   #11
Master Electrician
I don't see a bonding screw in your photo. Is this the first disconnect off the meter? Is it behind the red wires on right side? Main or only panel in the house?
Old 04-04-2010, 09:32 AM   #12
Master Electrician
QO and Homeline Square D are probably not the same number but I'm not sure. I will try to look them up.
BTW, what size wire are you using for the new sub. Those buss connections will accept up to a #4 conductor. Additionally, do you have sapce for a 2 pole breaker to feed the new sub?
Old 04-04-2010, 09:58 AM   #13
Master Electrician
SQ D Homeline # LK70AN for # 14- # 4, # LK 100AN #6-2/0
Old 04-04-2010, 12:16 PM   #14
thanks for all the replies
This is the only panel in the house. Yes, its a mess but it's not a mess of my making
no, there is not space for a Double Pole, but the whole point in adding a subpanel is to free space from the main and move them down to the subpanel. By doing so, the mess you see will be substantially cleaned up.
@secutanudu - The lug you show in the picture is exactly what the new Homeline SquareD sub panel I bought has. My main does not have one, but its good to know they are purchasable.
The thickness of the wire is cooper which is rated at 95A, I can't remember exactly but I think it was #2 conductor (Black outter shell, each conductor has 7 individual strands, except for the green grounding wire that is much smaller)
Russell
Old 04-04-2010, 12:25 PM   #15
Master Electrician
that's an understatement....that thing is absolutely disgusting.
andrew79 is offline   Reply With Quote
Main disconnect neutral wiring Daniel Holzman Electrical 5 10-04-2009 01:36 PM
Adding a subpanel BimmerRacer Electrical 20 04-01-2009 08:30 PM
add subpanel or replace main panel... red86yota Electrical 3 12-04-2008 09:43 AM
Help if it's not too late!! Cyndi Electrical 255 10-10-2008 09:18 PM