Adding A Lighting Circuit For The Basement, Maybe Some Other Changes. - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-23-2012, 07:49 PM   #16
ffemt121's Avatar
Originally Posted by k_buz
Barring local amendments, the 2008 code requires all basement recepts to be GFI protected. There is no exception for single recepts or above 7'.
Thanks, when I rip out the walls, I will replace the boxes and outlets. If all the receptacles are on the same circuit, I only put one at the head of line right?
ffemt121 is offline   Reply With Quote
Old 10-23-2012, 07:54 PM   #17
ffemt121's Avatar
Also, do I need to put GFCI or AFCI breakers in the panel to protect the stuff down there? I just had the panel replaced and it passed rough a s final with no GFCI or AFCI breakers
Old 10-23-2012, 08:15 PM   #18
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
If your are not adding any additional wiring or devices GFI or AFCI not required.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 10-23-2012, 09:22 PM   #19
ffemt121's Avatar
So then if I am running new home runs to put stuff on it's own circuit I do need to then? Correct?
Old 10-23-2012, 09:29 PM   #20
DIY Enthusiast
sublime2's Avatar
Rewards Points: 504
Does this apply if the basement is finished?
sublime2 is offline   Reply With Quote
Old 10-23-2012, 09:55 PM   #21
Licensed electrician
Rewards Points: 1,892
Receptacles in the unfinished portions of the basement require GFI protection. A finished basement does not.
The Following 2 Users Say Thank You to Jim Port For This Useful Post:
ffemt121 (10-23-2012), sublime2 (10-23-2012)
Old 10-24-2012, 07:01 AM   #22
electures's Avatar
Originally Posted by stickboy1375 View Post
This would depend on what code cycle the OP is on... 2005 I believe is the only code cycle that allows this.
The OP lives in New Jersey. Here is a thread I started for New Jersey. Post #14 addresses GFI protection specifically. Additionally, the work falls under the Re-Hab subcode which modifys some of the NEC requirments as well.
The Following User Says Thank You to electures For This Useful Post:
ffemt121 (10-24-2012)
Adding an outside lamp to a circuit??? CoconutPete Electrical 5 07-26-2011 03:54 PM
Adding Circuit for basement remodel ksl Electrical 3 01-10-2011 08:58 PM
adding a new circuit breaker panel Lana65 Electrical 0 09-23-2010 04:39 PM
Checking circuit load for recessed lighting Nathan0115 Electrical 12 05-07-2010 03:49 PM
Adding new circuit breakers to 100 amp sub panel DrP Electrical 8 05-25-2006 10:05 PM