Adding an electrical outlet box


Hi guys,

I need to add an electrical outlet on an Island I built. It is sheetrocked already and I was wondering if those electrical boxes for old work with the lillte ears are good. I don't want the outlet box to loosen over time. The sheetrock is 1/2 inc, should I use one of those boxes, or should I cut out a piece of sheetrock and add the outlet box screwed to the stud? Thanks

Advertisement

helpless handyman is offline   Reply With Quote
Old 06-07-2007, 10:53 PM   #2
remodeling pro
 
Join Date: Sep 2006
Posts: 1,399
Rewards Points: 500
Default

Adding an electrical outlet box


The "old worK" boxes are ok, but if you can locate the side of the stud, I would remove the factory installed nails and their little holders from a soft plastic nail on, and cut the hole so that it slips right on side the stud. Predrill a couple of 3/16" holes at the top and bottom corners, then send in a couple of 1 1/2" drywall screws.

Advertisement

troubleseeker is offline   Reply With Quote
Old 06-08-2007, 06:57 AM   #3
Licensed Electrical Cont.
 
Speedy Petey's Avatar
 
Join Date: Feb 2004
Location: NY State
Posts: 6,904
Rewards Points: 2,162
Default

Adding an electrical outlet box


Old work boxes are perfectly fine. I use them ALL the time.

If you are not comfortable with them you can use a Smart Box. This is a box designed exactly as trouble described, but is legal for the application.
__________________
Sometimes I feel like if I answer any more questions it is like someone trying to climb over a fence to jump off a bridge and me giving them a boost.
Answers based on the 2008 & 2011 NEC.
Speedy Petey is online now   Reply With Quote
Old 06-08-2007, 07:34 AM   #4
Member
 
RippySkippy's Avatar
 
Join Date: Feb 2007
Location: Ames, Iowa
Posts: 1,233
Rewards Points: 500
Default

Adding an electrical outlet box


they work well...just make sure you don't make the hole too big....not that I would know anything about that....
RippySkippy is offline   Reply With Quote
Old 06-08-2007, 09:16 AM   #5
Member
 
Join Date: Jul 2006
Posts: 729
Rewards Points: 500
Default

Adding an electrical outlet box


Thanks alot guys for the Great responses. I like the smart box, but I see they are plastic and in NY only metal is allowed with bx cable.

Thanks,
helpless handyman is offline   Reply With Quote
Old 06-08-2007, 03:56 PM   #6
Licensed Electrical Cont.
 
Speedy Petey's Avatar
 
Join Date: Feb 2004
Location: NY State
Posts: 6,904
Rewards Points: 2,162
Default

Adding an electrical outlet box


Quote:
Originally Posted by helpless handyman View Post
I like the smart box, but I see they are plastic and in NY only metal is allowed with bx cable.
Says who? Check your sources.
__________________
Sometimes I feel like if I answer any more questions it is like someone trying to climb over a fence to jump off a bridge and me giving them a boost.
Answers based on the 2008 & 2011 NEC.
Speedy Petey is online now   Reply With Quote
Old 06-08-2007, 06:19 PM   #7
Member
 
Join Date: Mar 2006
Posts: 682
Rewards Points: 500
Default

Adding an electrical outlet box


If we really are talking about BX cable (listed in the code as type AC) then how would one ground it without a metal box.

We are probably really talking about type MC cable. How would one bond the metal sheeth without a metal box and fittings?
__________________
Master Electrician
jwhite is offline   Reply With Quote
Old 06-08-2007, 06:42 PM   #8
Master Electrician
 
JohnJ0906's Avatar
 
Join Date: Mar 2007
Location: Baltimore, MD
Posts: 332
Rewards Points: 250
Default

Adding an electrical outlet box


314.3
You would need an internal bonding means to use a plastic box with MC cable.
__________________
John from Baltimore
One Day at a Time
"Experience is what you get when you were expecting something else"
"The bitterness of low quality lingers long after the sweetness of low cost is forgotten"
JohnJ0906 is offline   Reply With Quote
Old 06-08-2007, 07:45 PM   #9
Member
 
Join Date: May 2007
Location: NC
Posts: 88
Rewards Points: 75
Default

Adding an electrical outlet box


I have good luck with plain ol "old work" boxes if they are safe in your state. You have to tighten them well (but not too well) and they are nice and solid.
__________________
"Good judgment comes from experience. Experience comes from bad judgment."
keyser soze is offline   Reply With Quote
Old 06-08-2007, 09:01 PM   #10
Licensed Electrical Cont.
 
Speedy Petey's Avatar
 
Join Date: Feb 2004
Location: NY State
Posts: 6,904
Rewards Points: 2,162
Default

Adding an electrical outlet box


I didn't mean to imply he should use a plastic box with AC/MC/BX. Only that NM is no longer prohibited in NYC.
__________________
Sometimes I feel like if I answer any more questions it is like someone trying to climb over a fence to jump off a bridge and me giving them a boost.
Answers based on the 2008 & 2011 NEC.

Last edited by Speedy Petey; 06-09-2007 at 08:59 PM. Reason: typo
Speedy Petey is online now   Reply With Quote
Old 06-09-2007, 12:09 PM   #11
Member
 
Join Date: Mar 2006
Posts: 682
Rewards Points: 500
Default

Adding an electrical outlet box


Quote:
Originally Posted by Speedy Petey View Post
I didn't mean to imply he should use a plastic box with AC/MC/BX. On that NM is no longer prohibited in NYC.

Oh, I have no idea what is prohibited in NYC. My sister and her husband live on Long Island and romex is now allowed there.
__________________
Master Electrician
jwhite is offline   Reply With Quote
Old 06-09-2007, 08:59 PM   #12
Licensed Electrical Cont.
 
Speedy Petey's Avatar
 
Join Date: Feb 2004
Location: NY State
Posts: 6,904
Rewards Points: 2,162
Default

Adding an electrical outlet box


NM was always (basically) allowed on LI. I grew up there and started in the trade down there.

"The City" recently adopted an amended NEC and Art. 334 was left in with some changes.

Here is the official statement:
http://www.nema.org/stds/fieldreps/c...20073107ny.cfm


Here is what the Ammended Art 334 says:

Quote:
ARTICLE 334
Nonmetallic-Sheathed Cable: Types NM, NMC, and NMS

SECTION 334.10
Section 334.10 - Revise to read as follows:

334.10 Uses Permitted. Type NM, Type NMC, and Type NMS cables shall be permitted to be used in the following:

(1) One- and two-family dwellings.
(2) Multifamily dwellings, except as prohibited in Section 334.12.

FPN: See Section 310.10 for temperature limitation of conductors.

SECTION 334.12
Subsection 334.12(A)(1) - Revise to read as follows:

(1) In any multifamily dwelling exceeding three floors above grade.

Subsection 334.12(A)(11) - Add a new subsection 334.12 (A)(11) to read as follows:

(11) In non-residential buildings.

SECTION 334.30
Sub-Section 334.30(C) Delete in its entirety.
__________________
Sometimes I feel like if I answer any more questions it is like someone trying to climb over a fence to jump off a bridge and me giving them a boost.
Answers based on the 2008 & 2011 NEC.
Speedy Petey is online now   Reply With Quote
Old 06-10-2007, 06:10 PM   #13
Newbie
 
Join Date: May 2007
Posts: 1
Rewards Points: 10
Default

Adding an electrical outlet box


I always like a metal box to use.

Christopher Freville
andrew1978_us is offline   Reply With Quote
Old 07-06-2007, 07:46 PM   #14
Newbie
 
Join Date: May 2007
Posts: 18
Rewards Points: 10
Default

Adding an electrical outlet box


Quote:
Originally Posted by Speedy Petey View Post
Old work boxes are perfectly fine. I use them ALL the time.

If you are not comfortable with them you can use a Smart Box. This is a box designed exactly as trouble described, but is legal for the application.
What are the code requirements for attaching a box to a stud? Would it be against code to drill a hole in the side of a metal gang box and put a screw in at an angle?

I was told to be carefull using old work boxes in the bathroom and that attaching to the stud was much better, but also was told that screws or nails need to be in the back third of the box where there are already holes to prevent the risk of the screw head tearing away insulation on one of the wires. I don't see how I could get a nail or screw back there, with only 2" of width, so i was thinking of drilling a hole a third of the way in, and driving a screw at angle into the stud. I would think I could get the screw almost all the way in and that it would be out of the way.

I had originally looked for something like the smart box, but wanted metal, as I am trying to avoid PVC as much as possible due to the enviromental concerns (I know romex has pvc, though I heard there are some alternates, would love to hear of those). I saw this http://www.aifittings.com/whnew78.htm, which seems very similar to the Smart Box, but doesn't list material.

I really would appreciate any advice on this, and any explanation of the code on this.

Thanks
pacifier1er is offline   Reply With Quote
Old 07-06-2007, 08:59 PM   #15
Licensed Electrical Cont.
 
Speedy Petey's Avatar
 
Join Date: Feb 2004
Location: NY State
Posts: 6,904
Rewards Points: 2,162
Default

Adding an electrical outlet box


If the box is not designed to have screws through the sides it would be a code violation to do so. Do we sometimes do just that, I'll admit yes, once in a blue moon. Now with Smart Boxes and One Boxes though there is very little reason to do so.

Metal boxes with NM cable, hey, whatever floats your boat. I hate them, for several reasons. Capacity is one of the main reasons. Clamping is another.

PVC? Environmental concerns? NO COMMENT, on the grounds I don't want to insult anyone.....much. Sorry, I hear this *#@% all the time from folks in a town not too far from me. The same ones who scold me for eating meat.

If you are worried about the PVC box burning if the house catches fire, the small amount of PVC that is the electrical boxes is the last of your concerns. I'd worry WAY more about the chemicals under your sink and the paint cans in the basement.
There are also fiber boxes. Or bakelite. There is more than just PVC and metal, although I GREATLY prefer the grey PVC.

If you insist on using metal, use madison clips, or "box supports" for those not familiar with that term. I'm not sure who told you this is a bad thing in a bathroom.

Advertisement

__________________
Sometimes I feel like if I answer any more questions it is like someone trying to climb over a fence to jump off a bridge and me giving them a boost.
Answers based on the 2008 & 2011 NEC.
Speedy Petey is online now   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical outlet hook up. helpless handyman Electrical 4 07-30-2007 09:18 PM
electrical outlet problem ? BEN17 Electrical 1 07-29-2007 07:23 PM
Adding an aditional outlet outside question BCULP2 Electrical 13 06-27-2006 12:00 AM
Adding garage outlet Shane Electrical 1 02-23-2006 05:43 PM
moving an electrical outlet bobo Electrical 4 05-21-2005 01:15 PM




Top of Page | View New Posts