Adding 2 Circuits From Main Panel to Shed
I want to have 2 circuits in my shed. I have 7 open spots in the load center in the house. I need to know what I need and need to do to accomplish this. I assume that I will need a UF/B type of wire to run from the load center to a spot in the shed that will have a sub-panel. From that sub-panel I plan to distribute those two dedicated circuits out to two separate outlets inside of the shed.
I need to know what materials to purchase and how the wiring needs to be done in the load center and the sub-panel. Can someone assist?
09-19-2012, 09:56 AM
#2
Lic Electrical Inspector
WHat are they supplying? If it is just receptacles and lighting, 12/3 UF will give you 2 circuits (MWBC), but without the need for a panel suitable for use as service equipment.
All responses based on the 2011 NEC.
If you live in New Jersey click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . All other states click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. .
Please check with local, county and state officials as laws may vary.
Sizing motors To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online motor calculator To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online calculators To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. .
09-19-2012, 10:44 AM
#3
they are supplying two separate dedicated circuits that will be used for outlets and lighting.
09-19-2012, 11:02 AM
#4
12/3 UF on a two pole breaker. If the circuit is GFI protected it can be 12" deep. Non GFI has to be 24" deep. If you are trenching I would run PVC conduit and run cable through the conduit. Lighting does not require GFI. Receptacles require GFI.
09-19-2012, 11:21 AM
#5
You gonna mention a disconnecting means....
The Following User Says Thank You to Code05 For This Useful Post:
09-19-2012, 11:22 AM
#6
Licensed electrician
Except for a sleeve, I certainly would not want to pull UF in a conduit.
09-19-2012, 11:24 AM
#7
Geeze. I wanted to save something for somebody else. Thanks for the pick up.
09-19-2012, 11:45 AM
#8
So assuming the "shed" is detached, would that require a seperate ground rod and disconnect? I assume people do the 12/3 all the time and don't have issues but wouldn't code compliance be better?
09-19-2012, 01:19 PM
#9
Disconnecting means, yes. 225.31 NEC
Ground rods or other electrodes, no, if it is a single Multiwire Branch Circuit and contains an Equipment Grounding Conductor. 250.32 NEC.
09-19-2012, 01:20 PM
#10
Licensed Pro
The MWBC (12/3) would not require a separate grounding electrode. It would require some type of disconnect at the shed.
09-19-2012, 01:35 PM
#11
Beat you by 10 seconds....
09-19-2012, 02:36 PM
#12
What version NEC has been adopted in your local?
09-19-2012, 03:35 PM
#13
Thanks for the clarification. I guess I was confused on it being a MBC and not a small sub panel.